Current Transformer & Energy Meter Connections For a Changeover System

10/17/2012 4:31 AM

There is 250A LV switchboard with 2 incomers having Auto changeover Facility. there is no buscoupler. The client has given the CT & Fuse Connections (for Energy Meter),for each source, at the downstream of the breakers and fuses for voltmeter at the upstream. Now since it is a autochangeover , shouldn't the CT be in the upstream of the breaker? bcoz if the second breaker opens and the first breaker is closed , the current would flow through the bus containing the CT.

Kindly Advise.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Current Transformer & Energy meter connections for a changeover system

10/17/2012 8:05 AM

It does not matter (from a current measurement perspective) whether the CTs are on the line side (upstream) or load side (downstream) of the main breakers. When a breaker is open, no current will flow through it or the stub of busbar connecting it to the main bus.

The current will flow through the closed breaker(s) to the loads. Current needs a circuit to flow, so it won't "run upstream" and bump up against the open breaker to be measured in your CTs. Draw a 3-phase diagram of your system and add arrows for the currents that will flow when one main breaker is open, and you will see.

__________________
To get the right answers, first you need to ask the right questions.
Reply Score 1 for Good Answer
Anonymous Poster #1
#2
In reply to #1

Re: Current Transformer & Energy meter connections for a changeover system

10/17/2012 8:26 AM

But the voltage will exist . Kindly Refer the schematic which i uploaded and let me know.

Reply
3
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3
In reply to #2

Re: Current Transformer & Energy meter connections for a changeover system

10/17/2012 11:35 AM

Yes, there may be voltage, but the energy meter needs both amps and volts to show watts. As long as current = 0, watts will equal 0. CTs don't respond to voltage, so they will have 0 amps output for an open breaker condition (line current = 0).

Your energy meter cawill work fine on either side of the breaker (line or load), and your vendor is probably giving you what is either the most common configuration for them, or else what is easiest to build or fit into the enclosure.

__________________
To get the right answers, first you need to ask the right questions.
Reply Good Answer (Score 3)
Guru

Join Date: Aug 2007
Location: Indiana, USA
Posts: 579
Good Answers: 61
#4
In reply to #2

Re: Current Transformer & Energy meter connections for a changeover system

10/18/2012 8:19 AM

The previous comments are correct; the location of metering CT's in relation to the breaker doesn't matter (if they were for protection it would be a different matter).

There are two main reasons for the vendor to design this way. First, there's usually more room for CT and PT connections on the bus side of the breaker, when compared to the cable side. Second, the energy meter is most often a digital device which requires external power, usually obtained from the sensing PTs. As you indicated, there will always be voltage present, so the meters will have power for the display, datalogging and any electronic communications.

__________________
Experience: The knowledge you gain just AFTER you needed it.
Reply Score 1 for Good Answer
Active Contributor

Join Date: Sep 2012
Posts: 12
#5

Re: Current Transformer & Energy Meter Connections For a Changeover System

10/18/2012 10:35 AM

The CT/Fuse connections are okay as wired (downstream of each breaker).

If the connections are installed UPSTREAM OF EACH BREAKER, even if the current is ZERO (because circuit breaker is opened), the ENERGY METER will still read something (because it will still read VOLTAGE). Thus the ENERGY METER reading will NOT BE ACCURATE.

Hence the connection downstream of each breaker is CORRECT.

Reply Score 1 for Good Answer
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Olu Gyibrilla (1); PeterT (2); pwr2thepeople (1)

Previous in Forum: Sensor Transducer   Next in Forum: Cables and Lugs

Advertisement