Anonymous Poster #1

Harmonic Measuremnt

10/22/2012 8:51 AM

I have some harmonic values from a HV system. They were measured based on the IEC standard. My concern is this: I have values such as mininum, average, and maximum( i.e. Vrms.) within the time interval of 10 minutes, which level I should use to evaluate the maximum permisible level as specified in the IEC (IEC call them compatibility values).

For instance: within 10 minutes window I got the following values for the 5th harmonic

Minimum 1%

average 5%

maximum 8%

then the IEC limit is 6%. So should I say that the 5th harmonic is out of range based on the maximum value or is within ragen based o the average value?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Harmonic Measurement

10/22/2012 9:13 AM

One should go by the max. value.

Reply Score 1 for Good Answer
Participant

Join Date: Jul 2012
Posts: 2
#2

Re: Harmonic Measuremnt

10/26/2012 9:43 AM

The compatibility levels described in IEC standards should be considered as long term limits. the exact statement is:"by convention, the compatibility level is chosen so that there is only a small probability that it will be exceeded by the actual disturbance level".

So, if the maximum value of 5th harmonic voltage (8%) is observed during short times, everything is OK.

Generally, the Power Quality is assessed by using statistical analysis. For example: 95% of the 10 minutes measurements during a given period must be below the maximum limit.

Check EN50160 (Voltage characteristics of electricity supplied by public electricity networks) for more information.

Reply