Fail Safe Terminology

10/27/2012 3:47 AM

Can anybody explain what is meaning fail safe start command to DG set?

The DG set is connected to EMCC (Emergency switchboards)

EMCC has two Incomers, Incomer -1 as normal incomer & Incomer-2 Emergency (DG-set) in normal case

1) When there is power fail-

Start command is generated at EMCC ( By monitoring Line & Bus voltage) & given to DG set ( AMF panel) which in turn give Engine start command.

After voltage built up Automatic forward transfer happens (Transfer of loads on DG).

regards

Rodrick

Register to Reply
Pathfinder Tags: Fail safe
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Fail safe terminology

10/27/2012 7:53 AM

May I put a counter question? What is the plain dictionary meaning of "fail safe start command."

Register to Reply
Participant

Join Date: Oct 2012
Posts: 2
#2
In reply to #1

Re: Fail safe terminology

10/27/2012 11:53 PM

Dear Joshi..

Please note that Fail safe in Electrical system can explain like this

Fail safe equipment if fails than also there is no harm or it is safe.The couples eg are-

1) Stop command is always "open to stop type" i.e. "in Electrical Control ckt "NC contact is used of Pushbutton). SO that in event of failure of stop Pushbutton element or damage of remote cable core (incase remote Start /stop is anticipated ) the Motor /equipment shall stop automatic or Motor /equipment cannot be started again as per safety aspect.

2) In case of Electromechanical Brakes of 24V/110V/220V D.C in system brake is released when the Coil is energies & Brakes shall be engages when D.C supply is disconnected. In case if coil failure also the brake will be engages.

There are many eg of that kind.

I hope it is clear to you.

Similarly for the DG start what ???

( Since DG should always start in the event of Power fail) but how ???

Regards

Rodrick

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#3
In reply to #2

Re: Fail safe terminology

10/28/2012 12:24 AM

Thank you, rodrick. I follow you now.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#5
In reply to #2

Re: Fail safe terminology

10/28/2012 1:33 AM

The link DNV-OS-A101 posted else where, is not exactly what you are looking for. But it is about the 'fail safe principle' Please see under SECTION 5 EMERGENCY SHUTDOWN (ESD) PRINCIPLES, C. Fail-Safe Functionality.

Register to Reply
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#4

Re: Fail Safe Terminology

10/28/2012 1:00 AM
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6

Re: Fail Safe Terminology

10/28/2012 4:26 AM

Rodrik

From the definitions so far obtained for 'Fail Safe', it seems that, here, it might mean:

"The starting contact does not need a powered device (like a relay or contactor) to be energised before making and starting the DG" (?)

i.e. When there is power failure, a coil is released and a N.C. contact on this coil, will start the DG engine.

Does it make sense ?

Register to Reply