Re: Short Circit of Secondary side of Transformer.
10/31/2012 8:05 AM
If you don't know the fault level on the primary side (from the utility source) to calculate through the transformer, you can do a quick approximation by dividing Full Load Amps (FLA) by the impedance as a decimal:
(kVA / (kV x √3)) / (%Z / 100)
For example, for a 1000kVA transformer at your specified voltages, secondary FLA is 1391 amps. Impedance is 5%, so max fault current is 1391 / 0.05 = 27824 amps (approximately). A more detailed analysis would have to be done to get a more accurate number, but usually this is adequate for estimating equipment ratings.
Note that this does NOT take into account the contribution from other devices downstream that may feed energy back into a fault, such as motors.