Load Cell Connection

11/07/2012 3:41 PM

How can i connect load cell to plc , can it connect directly to analog port in plc without amplifier?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#1

Re: load cell connection

11/07/2012 4:06 PM

The load cell documentation cannot be seen from Fargo, USA. What does the documentation of the load cell say about this?

__________________
Semper Ubi Sub Ubi
Reply
3
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: load cell connection

11/07/2012 4:21 PM

One connects them with wires!

(Can I get a rim-shot!)

Ahem, excuse me that was a little too frivolous of a response.

The nominal method for interconnecting any analog transponder to a Programmable Logic Controller (PLC) is through the combination of materials with both no and many free valence electrons available in their outer orbital shell. (insulators and conductors) The free valence electrons should be allowed to easily move from transponder to PLC while a layer of the material with no valence electrons separating the free valence material to prevent a short circuit path. This will maintain signal integrity. Now depending on the magnitude of the anticipated signal from the transponder and the sensitivity of the PLC receiver (facts neither presented or referenced here) one may wish to incorporate various semiconductor materials in the form of either a Whetstone bridge or amplifier circuit with the appropriate choice of power and resistive elements. Often one must consider in these cases incorporating some form of Nyquist filter networking to prevent signal aliasing effect from obscuring information. In many cases a transponder may already provide a conditioned signal format (4-20mA, RS232, RS422, BISS, etc.) that can either preclude analog to digital conversion or already provide Nyquist filtering. In these cases one likely need not provide anything but a contiguous valence path.

Alas once again, the critical pertinent information of transponder signal and PLC input sensitivity prevents the correct interface to be determined.

Go fish.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 3)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#3
In reply to #2

Re: load cell connection

11/07/2012 4:26 PM

Press for Rimshot

Well, that sort of worked...

How about: Press button in next window for Rimshot.

__________________
Semper Ubi Sub Ubi
Reply Score 1 for Good Answer
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Load Cell Connection

11/07/2012 4:54 PM

Unlikely.

The reason for the amplifier is to amplify the small signal generated by the small change in resistance of the load cell to a level that can be easily measured. It is highly unlikely that the signal level will be high enough for the PLC input to even measure let alone provide an accurate load cell measurement range.

Check the PLC and load cell data sheets for more details on the signal levels you are trying to deal with.

__________________
jack of all trades
Reply Good Answer (Score 3)
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Load Cell Connection

11/07/2012 5:24 PM

Yes, You can. I see by the data sheets for your equipment that amplifiers are not required for short runs.

The maximum, un-amplified length cable that you can use at your operating frequency is 1 inch.

Cheers.

Reply Good Answer (Score 2)
Power-User
Engineering Fields - Control Engineering - Newby Member Long Time User Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jun 2006
Posts: 224
Good Answers: 9
#6

Re: Load Cell Connection

11/07/2012 5:37 PM

That is dependent on the supporting Input modules of the PLC manufacturer.

Doing a google search shows that Omron has hardware that supports this function.

http://www.omron-ap.com/product_info/F159/index.asp

If you have an Omron PLC you may be able to plug the load directly into the module. However, most manufacturers PLC modules for mV input do not supply the stable excitation voltage required for load cells.

Obviously, you will need to check your PLC manufacturer, and to ignore the scrappy replys from less-than-helpful commentors.

Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#7
In reply to #6

Re: Load Cell Connection

11/07/2012 5:44 PM

"Obviously, you will need to check your PLC manufacturer, and to ignore the scrappy replys from less-than-helpful commentors."

It is not obvious at all. If it were obvious, the documentation of the two devices would already have been referenced and this thread would not have been posted.

Further, I found the response from redfred to be refreshingly accurate; I may give him a GA vote just because he fussed.

__________________
Semper Ubi Sub Ubi
Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #6

Re: Load Cell Connection

11/07/2012 6:28 PM

Scrappy reply? Phooey.

I reserve the right to be helpful in a humorous or erudite fashion when insufficient information is provided in the Original Posting. I still stand by my initial curt answer. Wires must be used to connect between load cell and PLC. My verbose reply identified several plausible analog and digital interface types of load cells that will not require any additional signal conditioning. If and when the OP decides to help themselves by telling us which interface their load cell and PLC have, I will gladly help clarify what type of wiring and possibly signal conditioning they will need for an accurate reading.

Until then you will just have to find that old copy of Merriam Webster's collegiate journal to comprehend the delectable nuances of my use of the English language.

You may have your shovel back.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Good Answer (Score 2)
Guru

Join Date: Aug 2012
Posts: 1071
Good Answers: 92
#9
In reply to #8

Re: Load Cell Connection

11/07/2012 8:32 PM

Aren't you going to wash it first??

Reply Off Topic (Score 3)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11
In reply to #9

Re: Load Cell Connection

11/07/2012 10:38 PM

Nah, I like the exquisite yet pungent bouquet of fortified guano. I think it adds a certain level of colorful dignity.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Off Topic (Score 5)
Power-User

Join Date: Sep 2006
Location: Houston Texas
Posts: 282
Good Answers: 16
#10

Re: Load Cell Connection

11/07/2012 10:35 PM

If you want a crude and low-resolution method to connect a strain-gage directly to a PLC analog input, a thermocouple input would work.

__________________
Specializing in Dynamic Weighing Systems for Powder and Bulk Solids Handling
Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#12

Re: Load Cell Connection

11/08/2012 5:58 AM

Most load cells need an excitation voltage of 10volts and return a signal voltage typically around 3mV/V. Assuming that you PLC can deliver a stable 10V output (most PLC output at 24V +/- 1V depending on the attached load) you should be able to return 30mV at full range of the load cell. With a 0-10V input to the PLC this works in theory but you are only using 1/300th of the input range. This will be converted into a digital signal with let us assume a 12bit A-D converter. So instead of being able to resolve to 4096 steps you will only be able to resolve to 14 steps .

Now for the snags.

You cannot just use a dropper resistor to reduce the PLC output voltage to 10V as this will follow the voltage variations. A properly regulated 10VDC supply with low ripple is required. (This costs out at about the same price as an amplifier which has a regulated supply included)

You are probably not going to use the load cell over its full range, if you do you are in danger of overloading and destroying it. So if allow a safety factor of 2 your maximum output is 15mV. (reducing you resolution to 7 steps)

The output of your load cell is supposed to be linear, but in fact is isn't, a problem that would be corrected by the amplifier, but you don't have an amplifier. So you should analyse the non-linear input (you are looking for a six or seven function sine curve that you can derive using Fourier analysis) and then write a program to apply a correction (that might be quite hard as you only have a PLC, but it would be relatively easy in software like C++), but your input and resolution are so crude that this may not be worth the effort.

Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2010
Location: Tulsa, OK
Posts: 184
Good Answers: 2
#13

Re: Load Cell Connection

11/08/2012 9:35 AM

Yes you can connect a load cell to a PLC, now then come all the buts.

But the PLC analog input card has to have the capability to read the low level voltage signal.

But the PLC will need a special summing program since most load cells work several at a time averaging their measurements.

But the load cell faults are almost impossible to detect directly from a PLC input module.

And finally the accurate ranging of the load cell measurements are not easy to input into the PLC.

So the answer is Yes you can do it, and No you should not unless it is an experiment.

What you would be saving as less load cell summing card and transmitter you will pay out extra in the PLC part.

Reply
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

BDThompson (1); Delmar (1); Doorman (3); jack of all trades (1); jhhassociates (1); JNB (1); lyn (1); redfred (3); vargaalex (1)