Increase Capacitor Bank Capacity

11/20/2012 12:22 PM

I want to increase capacitor bank capacity, but I can't (200kvar TP 320 kvar) Increase the load because I already using full capacity of electric Power.(850A) full load. .if I increase capacitor bank ,will the ampere will rise. ? ,

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#1

Re: Increase Capacitor Bank Capacity

11/20/2012 1:46 PM

It will balance out. When you have a shut-down of some load, you try out additional capacitors & carry out a check on your Amps consumption, with/without additional capacitors.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Increase Capacitor Bank Capacity

11/20/2012 4:07 PM

What is your power factor at 850 amps? You need to know this before adding additional capacitors.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#3

Re: Increase Capacitor Bank Capacity

11/21/2012 11:40 AM

As #2 said, you need to check your existing load p.f.

If below 0.95 and the new increse of p.f. will not exceed the 0.95 (for safety), then your existing load will not increase the Amps drawn. The Amps will drop for the same kW consumption.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2012
Posts: 2
#4
In reply to #3

Re: Increase Capacitor Bank Capacity

11/27/2012 1:58 PM

Is the capacitor bank work on his own power? What it takes a current that not comes under full Load Current of overall factory?

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Joshi (1); LAA_Lucke (1); saishirdi (1); wareagle (1)

Previous in Forum: Power Systems Engineering   Next in Forum: Causes of Oil Leakages from Transformer Bushing

Advertisement