11/23/2012 1:42 PM
We have installed a remote seal transmitter (as a part of a differential pressure transmitter). The process material (where the pressure is measured) is solution of sugar, aroud 50% Brix. We have incorrect readings of level, due to formation of deposits of sugar that affects the working of the diaphragm seal of the instrument.
To solve this problem it was installed a flushing ring between the process flange and the measuring flange, but when we proceed to flush the level reading was incorrects again in a very short time.
So my question is if someone has information about why a diaphragm seal could fail. Is this about the pressure of the flush water, desing of the flush ring or other parameter?
Re: diaphragm seal of a pressure transmiter
11/23/2012 2:09 PM
Use an isolator between the gauge and the process fluid.
11/23/2012 2:49 PM
Re: Diaphragm Seal of a Pressure Transmiter
11/23/2012 5:52 PM
Is this a new installation?
Did it ever work acceptably, OK?
Was it orginally installed without flush rings? And the problem was ? ?
Immediately after flushing, how accurate is the level reading?
How big is the error after flushing? (example: drifts 40mm w.c. in 2 minutes after flushing)
What are you comparing the transmitter level reading to as a level reference? WHat level reading do you trust?
Are the level readings stable when the level is stable?
What are the LRV and URV values?
What is the tank height between the seal flanges?
11/24/2012 7:26 AM
What are the dimensions of the tank.
Where are the sensors located on the tank?
How critical is the level?
How critical is the Brix of the mixture?
What is the operating temperature?
What is the operating pressure(s)?(MINIMUM/MAXIMUM?)
What is the process liquid?
I can offer valid suggestions when I have the requested information.
11/26/2012 1:08 PM
it's an evaporator
at the suction of the recirculation pump and in the space above the level of liquid that accumulates the juice at the bottom
it's controlled around 40%
Very Critical
Around 70-80°C
400-500 mbar, it depends on the product
a sugar solution (long chains) of around 50 % Brix
11/26/2012 8:42 AM
What you have is build up of sugar on the external ridges of the seal, the only way you can eliminate this is to use a smooth faced seal, or install not a flushing ring but a flush with steam directly onto the face of the seal with a timer so it periodically cleans the seal face.
11/27/2012 8:43 AM
Thanks for the answer
Could I use a flush ring like the one on the next image for steam in place or this is not going to be applicated directly onto the face of the flush ring?
http://www.omicron.org.in/flushing-ring.html
Thanks in advanced.
11/26/2012 12:47 PM
Dawn, The Answer to your questions:
The flush ring was a new modification to wash the seal ring that exists at the beginning of the operations of the evaporator.
Yes, about a month after the flush ring was installed.
It was originally without flush rings, and the level readings were inaccurate, because the sugar in the solution solidifies.
It was accurate.
I can't answer, but when the sensor is clean, it works well.
We are comparing the level with the visual reading at the peephole.
Yes
About 20 ft
11/27/2012 10:10 AM
Your link shows a flushing ring (the Omicron). That's what I consider a flushing ring. So it isn't clear what it is that you have installed now that you call a flushing ring, if you plan on replacing it with the Omicron.
What do you have installed now, that you call a flushing ring?
11/27/2012 1:45 PM
Yes, We had installed a flush ring like the Omicron, but with 4 holes. My question was if this flush ring could be adapted to work with cleaning with steam
Location: OZ, otherwise known as Oklahoma were the wind comes sweeping down the plains.
Re: Diaphragm Seal of a Pressure Transmitter
11/27/2012 1:29 PM
Is the transmitter mounted at the bottom with the diaphragm facing up? Can the transmitter be mounted so the the diaphragm is vertical or facing down? It seems that solids settling out is your problem, and if you can mount the transmitter with the diaphragm in a different orientation it may solve your problem.
11/27/2012 1:46 PM
Thanks
The diaphragm is mounted vertically
11/28/2012 8:11 PM
I've been to Oklahoma many times.The wind quit blowing one day, and everyone in the state fell down.
11/28/2012 9:38 PM