Contactor Selection

11/26/2012 7:20 AM

Hello everyone, i have a doubt in contactors.

Actually i m need of a contactor whose coil rating is 48Vdc and contact rating is of 350A. My supply voltage is of 48Vdc (Battery).It is required for motor application of 48V(27V*3phase).

I had an Alright contactor of 48Vdc coil, Contact rating of DC-3 350A, 48Vdc. But this is presently not available in market. But for an alternate, i m not getting the similar rating of contactor for DC contacts.Actually there are contactors of 48Vdc coil, but its corresponding contacts are available for AC( ie. AC-3, AC-4,....).For a contactor with DC coil/contacts voltage rating should be less than corresponding AC voltage rating.

So my question is How can i replace a contactor having DC contacts and DC excitation(coil) , with, AC contact and DC excitation(coil), exactly? Is there any formula or standard, if so please reply immediately..........

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
6
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Contactor selection

11/26/2012 7:29 AM

DC power contactors are very special. At the power you mention, they are likely to have blow-out coils with massive arc chutes. Usually single or double pole configuration. Not very common, but available from Bhartia Industries, ABB, Schneider and maybe some others. Beware of bad copies, they can literally blow up. DC arc is very difficult to quench.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 6)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #1

Re: Contactor selection

11/26/2012 8:49 AM

KVS! I have a doubt on contactor Pick-up & Drop-off. IES 60947-4-1 Clause 7.2.1.2 mentions that 'contactors shall close satisfactorily at any value between 85% to 110% of their rated control supply voltage'.

Now, if I have a contactor with a 240V AC coil, the pick-up should be anywhere between 204 V to 264 V. If my contactor picks up at, say, 160V, does it pass the test or is it a violation of the above clause?

Similarly, I observed that the drop of is always within the band. For example, teh Standard says that for AC coils, the drop off is between 20% to 75% of Coil Voltage. (i.e.) for a 240V AC Coil, it is between 48V to 180V. But, I found that I always get somewhere around 80 V to 90V. Is it okay?

Register to Reply Score 2 for Off Topic
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #4

Re: Contactor selection

11/26/2012 9:55 AM

This one has caused me some problems too. The wording is taken by some testing authorities to mean that if a contactor picks up at 80% it is contravening this clause. Well, far from it. The clause means that the contactor MUST pick up when 85% voltage is applied to the coil. This should happen even if the coil is hot ! So, obviously, the cold pickup will be substantially less by design itself. i have gone hoarse explaining this to some test engineers, but fortunately, most of them understand the clause correctly.

Coming to the drop-off band, you know that it is extremely difficult to have a sharp drop-off when the voltage reduces. Airgap, remanent flux, coil temperature...many factors have a say in this. So, in their wisdom, the IEC experts have deemed that (a) it is impossible to have a sharp cut-off value,and that a band of drop-off voltage must be provided and (b) in reality, mostly the voltage will vanish to zero, rather than hover at a low value... a no-voltage rather than under-voltage situation is more realistic.

Many people (including me!) have designed solid-state triggered coils for contactors which have sharp cut-off, but that is worth another thread

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10
In reply to #8

Re: Contactor selection

11/26/2012 11:03 AM

Thank you, KVS! That is precise!

Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#2

Re: Contactor selection

11/26/2012 7:49 AM

Yes definetly KV sridhar, The Albright contactors do have blow outs to avoid arcing, but since it is not available, i have searched for Siemens and Schneider, but i hv not seen the similar contactors with DC contacts, i think they have only AC contacts. So i need to know if i can replace contactors of DC contact application with AC contacts.I need to have a definite approval before applying it..............

Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3
In reply to #2

Re: Contactor selection

11/26/2012 8:26 AM

"So i need to know if i can replace contactors of DC contact application with AC contacts."

No, you can't. It may work for a while, but if the manufacturer has not explicitly rated it for DC use at your working voltage and current and with your load type, it will almost certainly fail - possibly catastrophically.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11
In reply to #2

Re: Contactor selection

11/26/2012 1:29 PM

So i need to know if i can replace contactors of DC contact application with AC contacts.

In some situations yes, but you need to check the manufacturer provided documentation for DC operation de-rating and be aware that at currents as high as you are mentioning most contactors will not be suitable.

If it were me I would be looking at the supplier website and checking the contactors available, going up in contactor size until a suitable one could be found. Don't be surprised if you find that a suitable contactor has an AC current rating an order of magnitude or greater than its DC rating.

Additionally I would design and add snubber networks across the contacts to help with DC load arcing (but again only to increase the operational safety margin).

__________________
jack of all trades
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#5

Re: Contactor Selection

11/26/2012 9:21 AM

You sure of the name Albright International Manufactures DC contactors.

They still list a 350 Amp with coil voltages from 6 to 240v DC.

http://www.albrightinternational.com/lang/en/index.html

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#6

Re: Contactor Selection

11/26/2012 9:22 AM

What I would suggest is going to a continuous duty rated industrial machinery engine starter type solenoid/contactor.

There are a lot of big machines that run 48 volt DC systems with starters that draw well into the 1000+ amp range while cranking and their starter solenoids have no trouble what soever with breaking of those levels of currents at 48 VDC.

Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Contactor Selection

11/26/2012 9:34 AM

Search for the term "bar contactor", because at that power level, the arc chute is so long that the operating mechanism is rotary and the poles are connected by a bar that turns via lever action from the coil. Schneider got out of that business years ago I think, Siemens sold it off to another company, search for the name "Euclid", although they do still sell them through their transportation division, calling them "Railway C.ontactors" because that's the only market they see as viable. ABB still makes them as far as I know too. The applications are few and far between, so many people who used to be in that business have stopped due to lack of sales. And no, there is no way to use an AC rated contactor on DC at that current. AC contactors will have a DC current rating at 48VDC, but it is extremely low. For example an AC contactor rated for 350A AC may only be rated for 1 or 2A DC. You need the proper contactor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2007
Location: India
Posts: 1246
Good Answers: 34
#9

Re: Contactor Selection

11/26/2012 11:01 AM

For those that can help themselves.

Select your own contactor

Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#12

Re: Contactor Selection

11/27/2012 4:47 AM

I have seen in Siemens contractors of multiple poles that , if two or more poles are connected in series their voltage as well as current rating is increased. How come current rating increase?

For eg a 3rt1035 contactor has ratings

Coil : 48VDC

Contacts : AC-1/400V

• at 40 °C ambient temperature / rated value= 60 A

• at 60 °C ambient temperature / rated value= 55 A

AC-3 / at 400 V / rated value = 40A

at AC-4 / at 400 V / rated value = 35A

With 1 current path / at DC-1

• at 24 V / rated value 55A

• at 110 V / rated value 4.5A

With 2 current paths in series / at DC-1

• at 24 V / rated value 55 A

• at 110 V / rated value 25 A

With 3 current paths in series / at DC-1

• at 24 V / rated value A 55 A

• at 110 V / rated value A 55A

Here i m considering only DC section ie. DC-1 for 24V and 110Vdc at 1, 2 and 3 current path in series , as we can see for 110Vdc for 1 current path is 4.5A, for 2 current path in series is 25A and for 3 current path is 55A. Is this just their manufactured rating or is there any logic behind it?

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#15
In reply to #12

Re: Contactor Selection

11/27/2012 7:58 AM

s others have said, DC breaking is very sensitive to voltage. So, the more breaks there are in series, the better the breaking capacity. i give below an extract from a Siemens catalogue which hnestly depicts this. i hope it is readable. For example, a 3TB56 contactor can handle 400A @ 220V DC with three poles in series, but only 0.6A on a single pole !!! And practically nothing at all at 400V DC !!

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Score 1 for Good Answer
Member

Join Date: Apr 2012
Location: France
Posts: 7
#13

Re: Contactor Selection

11/27/2012 5:59 AM

Hello Everyone,

As mentioned in one of the post DC load are very difficult to break.

As you may be already know, the most important parameter in DC application is not current level, but DC voltage level on the load.

Bigger is the DC voltage on the load bigger will be the contactor.

As per Ayrton law each product get a specific arc voltage between his contact ( product design ).

This arc voltage is related to contact material use and distance between contact ( refer to Ayrton law for more details ).

To break safely DC load the arc voltage ( Technical data of product ) shall be bigger than load voltage.

Bigger is the difference ( 2 or 3 time ) faster we will break the voltage and in this matter you increase the electrical life time of your contactor.

Then in one post it is mentioned you do not find on big manufacturer ( Siemens and Schneider ) document on such product.

I will suggest in the Schneider product range ( if you DC load voltage is 48V it is not clear in your original question ) to use LC1F330ED ( This contactor is 48VDC coils and able to break 360A at 48VDC ).

You will find more details on Schneider web site http://www.schneider-electric.com/site/home/index.cfm/ww/ and in the MKTED210011EN catalogue in the DC table if you voltage load is different than 48VDc.

You may also use bar contactor which are quite efficient for DC application

You may also contact your Schneider country office and see with them what the best solution with your application is.

Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#14

Re: Contactor Selection

11/27/2012 6:26 AM

Actually i have already checked "LC1F330ED", but its contact ratings are for Utilization Categories AC-1 of 330A & AC-3 of 400A. But my load is an inverter driven Motor. Here connection is as follows:

Battery --> contactor --> Fuse -->Inverter--->Motor.

Here i do need a contactor of DC utilization category.

And please give a solution for my previous post ie. related to Siemens contactor also........

Register to Reply
Power-User

Join Date: Oct 2007
Location: S. California, USA
Posts: 279
Good Answers: 12
#18
In reply to #14

Re: Contactor Selection

11/27/2012 12:02 PM

With batteries capable of delivering 350A+, if contactor or wiring to the contactor faults, you have a big problem. I would put the fuse in front of the contactor and as close to the battery as possible.

Register to Reply
Member

Join Date: Apr 2012
Location: France
Posts: 7
#16

Re: Contactor Selection

11/27/2012 9:34 AM

The Contactor as also DC rating you will find them in the MKTED210011EN catalogue in page 5/205.

Nevertheless I strongly recommend you to contact your Schneider Office in your country

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#17

Re: Contactor Selection

11/27/2012 9:57 AM

So why not just use a large IGBT as a solid state contactor and be done with it?

Or for that matter why do you need a contactor anyway? does your inverter not shut down 100% when when the control circuits are turned off?

Register to Reply
Active Contributor

Join Date: Apr 2011
Location: Jamshedpur, India
Posts: 17
#19

Re: Contactor Selection

11/28/2012 2:10 AM

answer to the original problem mentioned by vipin:

use 2 nos of 24 V coil voltage auxiliary contactors. series their coil and supply 48 V to pickup. make suitable connections at their contact to supply 220 Ac for coil of a 350 A power contactor whose coil is 220 V ac. 220 V ac can be picked from plant lighting or as per ur wish. u can use 110 V ac also if it is readily available.

hope this may help to tackle the obsoletion.

Register to Reply
Commentator

Join Date: Aug 2011
Posts: 93
#20

Re: Contactor Selection

12/01/2012 1:25 AM

Thank you

Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (2); jack of all trades (1); JohnDG (1); Joshi (1); JRaef (1); JRPIRIS (2); kvsridhar (3); ozzb (1); Snave (1); sostoall (1); sujinvipin (4); tcmtech (2)