220 kV / 66 or 11 kV Step Down?

12/03/2012 9:19 AM

I working on a project with an area of about 5km X 2Km, My total power requirement would be around 200 to 300MVA. So m planning to have a 220kV Substation. My concern is which would be technically advisable:-

1. Stepping down 220kv directly to 11kv and feeding it the load centers through Ring Main units at various locations.

OR

2. Stepping down 220kV to 66kv and having three or four 66/11kV substations at different locations and from there feeding the load centers through Ring main unit.

Register to Reply
Pathfinder Tags: 220kv / 66 or 11kv?
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: 220 kV / 66 or 11 kV Step Down?

12/03/2012 1:38 PM

Is it my imagination or are questions getting a bit more out of hand and more into the realms of major country infrastructure engineering projects.

In my professional opinion, and forgoing a peer-reviewed feasibility and engineering study by a professional consultancy, go with 2. over 1. due to the power levels involved.

There, that probably saved you a few months and tens of thousands of dollars. Now you can press forward with getting a proper engineering design done and giving me a GA tick (or a cheque).

For best results include this CR4 thread in the final engineering design for peer review (specifically the second paragraph summary).

Jack - Your free engineering consultancy service.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: 220 kV / 66 or 11 kV Step Down?

12/03/2012 3:05 PM

10 out of 10 for imagination.

As we've gone along his projects become more fantastic.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: 220 kV / 66 or 11 kV Step Down?

12/03/2012 3:26 PM

Jack

I will give you a GA .

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4
In reply to #3

Re: 220 kV / 66 or 11 kV Step Down?

12/03/2012 3:52 PM

Thanks, this is probably the most expensive question ever asked (and answered) on this particular forum that I can remember.

__________________
jack of all trades
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Oct 2011
Posts: 95
#5

Re: 220 kV / 66 or 11 kV Step Down?

12/04/2012 5:46 AM

The area is 5x2=10 sq.km , seems to be big . But how the load will be distributed ?

2nd option seems to be better if load is not concentrated at one place.

Register to Reply
Member

Join Date: Aug 2011
Posts: 5
#6

Re: 220 kV / 66 or 11 kV Step Down?

12/07/2012 9:05 AM

You need substation and lots of 220kV-11kV step down transformer. 11kV feeders can deliver power in your 5km x 2km area. You need may be 10x11kV feeder to deliver 300MVA.

Register to Reply
Anonymous Poster #1
#7

Re: 220 kV / 66 or 11 kV Step Down?

01/09/2013 11:47 AM

What about 220KV/33KV instead of 220KV/11KV?

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); arifkunnath (1); Drton (1); jack of all trades (2); TonyS (1); wareagle (1)

Previous in Forum: CFL Ratings for Lamp Fittings?   Next in Forum: Looking for Linear Motor Cable

Advertisement