Flow vs Kv for a Pressure Regulating Ball Valve

01/15/2013 10:00 AM

For a pure gas constant downstream pressure control application valve Kv selected is 1330. Valve characteristics is 'equal percentage'. At 1415 cu.m/hr flow rate with 17 bar pressure drop, valve Kv is 95. Valve travel is 37% or 43 degrees. For same weight flow with only 1 bar pressure drop valve Kv is 438 and travel is 77% or 73 degrees.

I am interested to calculate maximum flow possible at full open with 17 bar pressure drop. Can any one help? Thanks in advance.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#1

Re: Flow vs Kv for a Pressure Regulating Ball Valve

01/15/2013 3:20 PM

Are you interested in calculating flow because your professor told you to?

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Flow vs Kv for a Pressure Regulating Ball Valve

01/16/2013 9:55 AM

No, I want to understand about sizing for a control valve based on the data available from valve data sheet.

Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#3

Re: Flow vs Kv for a Pressure Regulating Ball Valve

01/18/2013 3:05 PM

In theory, it would be fully-open Kv/95*1415. The pressure drop is the same for both cases and Kv is directly proportional to flow. You didn't give fully-open Kv.

But in practice it's more complicated. Published Kv figures are for valve in a pipe of the same size. Control valves are usually a size or 2 less than the pipe, and the Kv is multiplied by a swaging factor, typically 0.8, to account for the additional losses caused by the tapers. But 0.8 is somewhat arbitrary, and varies with valve opening, approaching 1 for small openings. When sizing a control valve I use swaging factor 0.8 for the max flow/min ΔP condition, 1 for the min flow/max ΔP condition (for safety, as that gives greatest range max Kv/min Kv, important for valve selection).

To complicate things further, if the ball valve is in a same-size pipe, when fully open the resistance is only about the same as in a pipe of same length. So depending on the system details there's likely to be more pressure drop in the rest of the system than in the valve itself.

Also there's the question of critical flow. It doesn't affect answer above as you only asked about flow at 17 bar ΔP, but if ΔP is more than about 0.5 x upstream absolute pressure, flow is sonic. You didn't give upstream pressure, but there's a good chance at 17 bar ΔP its sonic, at 1 bar ΔP its subsonic.

__________________
Give masochists a fair crack of the whip
Reply Score 1 for Good Answer
Anonymous Poster #1
#4
In reply to #3

Re: Flow vs Kv for a Pressure Regulating Ball Valve

01/20/2013 6:38 AM

Thanks Codemaster for a detailed answer, GA.

I could not get term "In theory, it would be fully-open Kv/95*1415". Can you please clarify? Here, I want to give some more information.

It's a caged ball valve and fully open Kv is 1330. Pressure drop in both cases are not same, it is 17 bar and 1 bar, but weight flow rate is the same. Upstream pressure in first case is 35 barg and in second case 19 barg, so it looks the flow is not sonic. Pipe size on both side are same as valve, 6".

Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #4

Re: Flow vs Kv for a Pressure Regulating Ball Valve

01/20/2013 10:43 AM

Your post says flow = 1415 cu.m/hr flow rate with 17 bar pressure drop, with valve Kv 95, and you want to calculate flow with fully open valve at 17 bar pressure drop.

Same pressure drop, so flow is proportional to Kv. For fully open Kv 1330, flow = 1330/95*1415 = 19800 cu.m/h. Perhaps you didn't mean that, but it's what it said.

Some more queries. Gas flow is usually stated at normal (0°C, 1 bara) or standard conditions (10, 15. 20 or 21°C depending on your taste, and 1 bara). They don't differ that much. But assuming any of them, Kv 95 for 1415 cu.m/h and 17 bar pressure drop is a long way out. I get somewhere near 95 by assuming it's actual flow at 36 bara. And you also mention weight flow.

To calculate Kv I take upstream pressure p1, downstream p2. Pressure ratio = p2/p1. Critical pressure ratio rc = 0.528 for air. Effective pressure ratio r for formula below = rc if p2/p1 < rc, and = p2/p1 if p2/p1 > rc.

Kv = Q/(p1*457)*√(T1/r/(1-r))

Q in Nm3/h, T1 upstream temperature K. This is for air, to avoid further complication.

I notice that for p1 = 36 bara, p2 = 19 bara, p2/p1 is spot on 0.528 = rc. This is probably not a coincidence, it looks like somebody has calculated p2 at critical pressure drop.

You can work it out from that, but come back if you need more (and clarify flow basis etc). You still need to take account of my #3.

__________________
Give masochists a fair crack of the whip
Reply Score 1 for Good Answer
Anonymous Poster #1
#6
In reply to #5

Re: Flow vs Kv for a Pressure Regulating Ball Valve

01/28/2013 11:24 AM

Many thanks Codemaster and GA.

I mean it (the value 19800 cu.m/hr), but it looks very high. At 43 deg valve travel it is 1415 cu.m/hr. Will the flow rate in ball valve after about half a travel can increase 14 times. I had calculated the actual flow at 35 barg pressure and 35 deg C. Nm3/hr is same in both the cases, that's why I mentioned same weight flow.

Now with your valuable comments I'm doubting whether full open Kv (1330) is right figure or not (it was taken from valve data sheet).

Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Codemaster (2); JPool (1)

Previous in Forum: ACCA and Manual J 8   Next in Forum: Effect Of Altitude On Pump Performance

Advertisement