Low Forward Power

01/22/2013 8:47 AM

Does low forward power protection of alternator will be in picture upto synchronising time only,then after rerverse power protection will take off the incase of reverse power in a alternator?

Register to Reply
Pathfinder Tags: llow forward power
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#1

Re: Low Forward Power

01/25/2013 9:19 AM

yes.

__________________
BNDas
Register to Reply
Active Contributor
Engineering Fields - Power Engineering - Thermal Power Plant Electrical Engineer

Join Date: Sep 2010
Location: INDIA
Posts: 18
#2
In reply to #1

Re: Low Forward Power

01/25/2013 1:42 PM

as low forward power and reverse power trip settings will be same normally.Then low forward power should ACT, at same time of Reverse power (even after synchronisation).

but at after synchronization only reverse power relay act for reverse power condition, why?

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#3
In reply to #2

Re: Low Forward Power

02/21/2013 3:07 AM

Low forward power as it is named see only forward power whether forward power is below some required flow so that motoring action doesn't happen specially during synchronisation. Thus it will remain vigilant for low forward condition. It will operate even during normal operation the power flow is less than required setting and acts before reverse power takeover.

__________________
BNDas
Register to Reply
Active Contributor
Engineering Fields - Power Engineering - Thermal Power Plant Electrical Engineer

Join Date: Sep 2010
Location: INDIA
Posts: 18
#4
In reply to #3

Re: Low Forward Power

03/08/2013 3:31 PM

thank you MR. Das

Normally after synchronization, during running any reverse power condition arises(due to low turbine speed or something..) REVERSE power relay will only trips but not low forward power right.