Underground Cabling

02/14/2013 12:02 AM

As per our under ground cable specification instructed as the H.V and M.V cables should not be laid in in the same trench can anybody tell me the reason for this practice

and and minimum distance for Segregation between them?

Register to Reply
Pathfinder Tags: Under ground Cabling
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Under ground cabling

02/14/2013 7:00 AM

NESC [C2-2007] Rule 353:

Minimum radial separation between any cable and other should be 300 mm [12 inches].

However, radial separation should be adequate to permit access to and maintenance of either facility to limit damage to the other.

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#2

Re: Under ground cabling

02/14/2013 7:10 AM

If your Instructions state Telcom cannot run in the same trench as LV/MV power then I would offer they have a safety policy for this whic states minimum clearances. However, it is not good parctice to run Telcom with or near power as either person from a utility can 'mistake' a cable and cut the wrong one open. Telcom not a hassle. LV/MV I think his eyes may tear up a little and a slight cooking may take place.

BUT, SCADA systems can run in the same jointing pit for connections, if needed and should be segragated from any power cables by means of a physical barrier. If works are being carried out on the power and fibres at the same time, then the power side would be dead and earthed down at the work area as well as at the ends, and breakers locked out.

I advise checking with your safety officer for clearances as they will differ country to country, Simple rule, If you can touch a live cable, or phase, your are probably too close for your own safety, (1100V=1.1kV. Are you meaning 11kV and higher?)

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#3
In reply to #2

Re: Under ground cabling

02/15/2013 2:23 PM

Sorry guys, i must be loosing it. I could have sworn the original questions was telcom cables in the same trench. My apologies. You can work on a simple 120mm separation per 10KV. Unless the cables are laid up to be in trefoil formation. the the trefoil phases can touch each other but the next set of trefoil should be the measurement above, 120/10kv. Look up Nexans, Olex, Prysmian, Pirelli web sites, they offer a load of information for their specific cable types. It is to do with heating, capacitances, dissipation of heat from cables, induction and fault currents. And it all depends on the cable type being used, the soil type the cable is buried in and load cycling on the cables. The above manufacturers have lots of details on cable clearances which is normally downloadable. No idea why I originally read this as telecom and 1100V. Sorry guys!