Flare Gas Meter

02/17/2013 9:58 PM

Hi, I am relatively new to instrumentation. I would like to seek advice regarding some issues we have on our plant. We just upgraded our flare gas metering system from the obsolete model of Fluenta--FGM130 to FGM160, however upon completion of the upgrade, we are encountering high fluctuations on our readings which we never experienced from the old model, FGM130. My question are: First, what can cause these fluctuations to occur? We experience the fluctuations during the hottest time of the day, and there are less/minimal fluctuations during night time and whenever it is raining. Second, we have noticed that there are inconsistencies on the wiring terminations of the transducers-- on the downstrean transducer, Blue wire is tagged as -IS where as on the upstream tansducer, the blue wire is tagged as +IS. I have asked the Fluenta service engineer regarding this, he said that the wire's color is not the basis for the correct termination, the taggings he said were correct and thus the termination is correct. I have some doubts, so if the current termination is incorrect, what would be its effect on our measurements?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Flare Gas Meter

02/18/2013 11:24 AM

There are so many things that could be happening here. I'm not familiar specifically with any technique used with flare gas monitoring so I will have to answer you in a generic fashion.

There maybe a loose or poor connection somewhere in the connection to the ultrasonic transducers. Troubleshooting where this type of an intermittent connection might be is the nightmare of any technician.

I also did a quick Google of your two models and noticed that both models are listed as a nebulous "fast response time" device. If the FGM160 is actually faster then possibly you are now seeing something that was ignored by the previous model. If this is the case then an authority in your company must decide if the gas flow must be corrected or if these fluctuations should be filtered out of the system.

Good Luck

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2011
Location: Sebastopol, California
Posts: 1205
Good Answers: 54
#2

Re: Flare Gas Meter

02/18/2013 11:10 PM

I have no experience with this either, but there is some correlation with light and dark conditions, or hot and cool.

Are the sensors using IR? Did they get re-aimed in some way? Is the new control board possibly incompatible with the sensor and requires a sensor upgrade as well?

Perhaps the sensor signal on the sensor is delivering a higher current or voltage than the new controller requires. It may be all you need is a series resistor in the line to reduce the sensitivity. If the new control board can "see" night and day differences when the old one did not, then I would suspect a sensitivity issue related to the sensor requirements of the new board.