I am trying to settle a debate. We have three Certified NABCEP PV installers on board, and three different opinions. I was hoping someone who was knowledable about PV module design could settle it.
An important and required task when designing a PV system is to adjust conductor sizing so that anticipated temperature range, conductor length, current, voltage, conduit fill and irradiance all are within accepted (mostly NEC) parameters.
Modules list maximum voltage at maximum power, which is always less than maximum voltage at open circuit. Conductors still must be designed to remain below 600 volts at all conditions, (with an additional safety derate).
Question, at open circuit voltage under standard test conditions (STC), does the open circuit voltage have the potential to increase as temperatures decrease, which is the case for all other conditions. Another words, is open circuit voltage a physical condition affectied by the mechanical construction of the cell, or is it also a dynamic measurement. I have never observed voltage above the rated open circuit voltage for a module, or for a series of modules (which is typical, as we like 400VDC strings)