Insulation Piercing Connector

03/05/2013 11:48 PM

TO supply electricity (230V AC) to terrace houses, the practice here is to run four (3p + n) insulated cables along the front of the terrace of houses. Cables are PVC insulated 35sq mm aluminium conductor. To connect each house, a tapping is made from one phase and neutral for single phase connection. The tapping cable is PVC insulated, either 35sq mm or 25 sq mm alumimium.

For the tapping connection insulation piercing connectors (IPC) are used of the same type used on Aerial bundled conductors (ABC).

We suffer a too high incidence of over heating and failure of these IPCs leading to loss of supply to the house. The loads are significantly lower (perhaps 15-25amps) than the rating of the IPCs (60-100A). We are aware that correct matching of the IPC to the conductors and correct torque when fixing the IPC are necessary to get good service.

Is anyone aware of a good alternative to using IPCs that is both easy to use, relatively low cost and gives good performance?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#1

Re: insulation piercing connector

03/06/2013 12:06 AM

Ask the cable manufacturers to recommend a suitable IPC.

__________________
pnaban
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #1

Re: insulation piercing connector

03/06/2013 10:24 AM

Get a well experienced technician to check the connection

__________________
pnaban
Register to Reply
Commentator

Join Date: Oct 2011
Posts: 95
#2

Re: insulation piercing connector

03/06/2013 1:16 AM

Check the connection. May be loose contact is causing the problem.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Insulation Piercing Connector

03/06/2013 9:36 AM

Something doesn't sound right. If you're working for a utility/contractor you should be able to present your problem to the IPC supplier who will work with you to understand the nature of your problem. If not then start searching for an alternate vendor who can supply something like this.

On the other hand if you're using a tap rated for ABC but not supporting it properly, then anything that allows either of the conductors to move (wind, street vibration, people, etc.) will accelerate the creeping of the al and ultimately cause a poor connection leading to heat cycling and ultimate failure.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 24
Good Answers: 4
#5
In reply to #3

Re: Insulation Piercing Connector

03/06/2013 7:42 PM

Thanks for the info on Michaud.

The IPCs are properly tightened on installation (using shear heads ). The connections are not subject to wind or other vibration

However my main question asks if there is a suitable alternative to using IPCs for these tap connections.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#6

Re: Insulation Piercing Connector

03/07/2013 8:16 AM

The most reliable method of joining two conductors together is called a CAD Weld.It melts the 2 conductors together to form one solid piece.No vibration or temperature issues with this connection.

Then there is the old but reliable split-bolt or parallel clamp connection.If properly installed can give years of trouble free service.

Reliability is paramount in your case, and repairs cost much more than doing it properly the first time.

Insofar as insulation-piercing connectors go, I would consult with the current manufacturers engineering dept to determine why their connectors are failing.I am sure they are as equally interested in learning the failure mode of the connectors as you are.

Good Luck!

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#7

Re: Insulation Piercing Connector

03/07/2013 8:33 AM

I tried to get this in under the edit time limit, but failed to do so.

Here is a link to the man that wrote the specs on IPC connectors, with instructional video.

http://www.youtube.com/watch?v=n75qR-eBx0c

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

arifkunnath (1); eugene344 (1); HiTekRedNek (2); pnaban (2); RAMConsult (1)

Previous in Forum: How to Confirm the Existence of Greases and Oil Seal Inside Motor w/o Dismantles   Next in Forum: Motor Generator Frequency Converters Manufacturers

Advertisement