03/14/2013 2:19 PM
2 active resistors each 10 Ohm. Phase voltage 220V, line voltage 380V.
220V Phase A --- R 10 Ohm ---Neutral ----R 10 Ohm ---220V Phase B
P = 2(220V*22A) = 9680W ?
or
P = 1.41*380V*22A = 11787W ?
Re: 2 Phase Power
03/14/2013 5:45 PM
Question for you. What is the amperage on the neutral?
Re: 2 Phase Power
03/15/2013 1:36 AM
Thanks for your answer, Waregle. Current should be both neither 22A nor 44A (if there were 3 phases and 3 equal loads then curr = 0). I always have had difficulties with these phasor calculations.
Good Answers: 181
Re: 2 Phase Power
03/16/2013 6:12 AM
In=(1/√(Ia²+Ib²))*100
Re: 2 Phase Power
03/16/2013 11:20 AM
Ampers in the neutral should be about 31A.
Then ,
P = 1.41*220*31?
I always thought we multiply the square root of 2 with line voltage and phase amperage (just like the sq root of 3 for 3 phase load) - now it seems we should multiply it with phase voltage and neutral amperage?
Re: 2 Phase Power
03/16/2013 1:25 PM
Since these currrents are 120 degrees apart, the neutral current must be added using vectors.
In = Ia @0 degrees + Ib @ 120 degrees.
In = 22 +J0 + (-22 cos 120 + 22 sin 120)
In =22 + 0 - 22 x .50 + 22 x 0.866 = 22 amps at 60 degrees.
Good Answers: 181
Re: 2 Phase Power
03/16/2013 5:45 PM
Are we talking about phases at 120° or 90°
Re: 2 Phase Power
03/17/2013 3:42 AM
Did not know it is so complicated. Thank you for answers. But, in any way, IS the power consumed 9680 W ?
Re: 2 Phase Power
03/17/2013 6:53 PM
The voltage give appear to be a wye connection.
Re: 2 Phase Power
03/18/2013 1:21 PM
Wye with neutral - 2 shoulders of which have each a resistor 10 Ohm. Phase to phase 380 V, phase to neutral 220 V.