Member

Join Date: Mar 2013
Posts: 5

Damage to Single Core Cables

03/18/2013 3:42 PM

Thankyou IQ for your detailed comments.

Just to let you know cable is non shielded, has no semi con, has a concentric wire shield of 2/0, wire shield was only connected to ground on the pole side, not at switchgear. They were connected together but isolated from ground at this end.

Cable Structure - PVC Jacket - Aluminum Interlocking Armour - Inner PVC Jacket - Concentric Copper Ground Wires - XLP Insulation - conductor shield ( not semi conductive) - and 750 MCM Copper Conductor.

What would be approx. sum of currents flowing in this case?

We do have some slack in cables and could do new terminations. Also this being a non shielded cable we can remove concentric ground wires back closer to top of gland entry point, bend wires back /cut & tape for isolation . Cable can be terminated without stress cones?

Please Comment. Again thanks for all comments. Electron.

Register to Reply
This discussion was "closed" on 03/18/2013 7:31 PM. No new comments are allowed.
Message from admins:
duplicate thread
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Damage to Single Core Cables

03/18/2013 3:58 PM

Why did you start a new thread???????

What's wrong with this one? Damage to Single Core Cables

Register to Reply
Member

Join Date: Mar 2013
Posts: 5
#2
In reply to #1

Re: Damage to Single Core Cables

03/18/2013 4:29 PM

Sorry made a mistake by starting this thread. Please disregard this thread and reply to orignal thread. Regards Electron

Register to Reply
Register to Reply 2 comments
This discussion was "closed" on 03/18/2013 7:31 PM. No new comments are allowed.
Message from admins:
duplicate thread

Previous in Forum: The Unexpected I   Next in Forum: Transformer Radio?

Advertisement