Hi
I have a problem in our Breaker trip circuit.We are using Siemens 7SJ62 relays for trip circuit supervision.The connections are as per diagram given in the relay manual using two Binary inputs and 52a & 52b Contacts.In this circuit the relay configured with a 19V DC selection(TCS Binary inputs only)The working voltage is 110VDC.
Now once the circuit is powered up we have done trip test in the following sequence.
The sequence of operation done
was as follows.
·
Close
CB
·
Push
the "CB OFF" Push Button.
·
CB
tripped.
·
Keep
the "CB OFF "Push button pressed.
·
Closed
CB
CB closed and tripped immedietely
Close The CB once again
CB closed but didn't tripped
We tried the same with the connection disconnected from 7SJ62 relay,The circuit works perfectly
I would like to know whether anybody got similar problem and what was the solution?