04/02/2013 6:33 AM

When u are adding a custom library for a relay (from the "library" menu at the top) in ETAP 7.0, at the "relay library: model" window , in the "model info" section,,,, there is a parameter called "current setting". The value of which is one of the followings:

0.2

1

2

5

2/5

1/2

1/5

1/3/5

0.1/1/5

0.2/1/5

0.03/0.2/1/5

etc

Are these the currents which the relay can read as an input? so that if i set the current setting of a relay to, for example, 0.03/0.2/1/5. Then does it mean that the relay will only read the input accurately when the relay amps (CT secondary side / relay input) is equal to 0.03, 0.2, 1, or 5 ampere? can anyone confirm about this

regards

__________________
vandie
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Active Contributor

Join Date: Dec 2011
Posts: 16
#1

Re: ETAP Question - Custom Library for a Relay

04/03/2013 9:25 AM

Your Question is NOT CLEAR

may be this will help

http://en.wikipedia.org/wiki/Relay

Register to Reply Off Topic (Score 5)
Associate

Join Date: Mar 2013
Posts: 39
#2
In reply to #1

Re: ETAP Question - Custom Library for a Relay

04/03/2013 12:42 PM

which part is not clear?

__________________
vandie
Register to Reply Off Topic (Score 5)
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: ETAP Question - Custom Library for a Relay

04/03/2013 7:17 PM

The current rating is the maximum input current that the relay can receive from the CT secondary. A relay can have only one current rating (such as 5) or multiple current rating (such as 1/5). If the current rating is multiple, the relay should have the option (either by programming or selector switch) to select the rating which one you want to use. For example, GE Multilin 469 relay has current rating 1/5 (see fig below):

In the "relay library: model" page of ETAP, you should select 0.03/0.2/1/5, only if the relay has four input current ratings, such as 0.03A, 0.2A, 1A and 5A. See the catalog of the relay that you are adding in the library and find the relay input current. Use the input current that the relay has in its catalog.

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Associate

Join Date: Mar 2013
Posts: 39
#4
In reply to #3

Re: ETAP Question - Custom Library for a Relay

04/05/2013 8:56 AM

This is the answer i've been looking for. Thx a lot msamad.

__________________
vandie
Register to Reply
Anonymous Poster #1
#5
In reply to #3

Re: ETAP Question - Custom Library for a Relay

04/05/2013 6:38 PM

By the way... forgive my ignorance. How do you to upload a pic to a post in this forum?just like what you did in the above post. I'm still a newbie here. Thx

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6
In reply to #5

Re: ETAP Question - Custom Library for a Relay

04/05/2013 10:17 PM

This is a genuine question, and hence no hesitation.

You can use the Insert/Edit Image icon (shown yellow highlighted below) to add a picture file.

You can use Windows 7 snipping tool (Start -> Snipping Tool) to capture anything from your screen and save it as a picture (such as .png file) and insert it in your post.

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Off Topic (Score 5)
Anonymous Poster #1
#7
In reply to #6

Re: ETAP Question - Custom Library for a Relay

04/06/2013 4:47 AM

No2,,i didnt know there was a toolbar there to upload a picture. Coz it did not appear in my browser when i was trying to post sumthing. Now i realize i just had to change my browser to another one...so now the toolbar is there ..my mistake... thank youuuu...

Regards,,

Register to Reply Off Topic (Score 5)
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); daveross100 (1); msamad (2); vandie (2)

Previous in Forum: Dead Time Constant of IGBT   Next in Forum: Single End Bonding with Surge Arrester for 6.6 kV Cables

Advertisement