Transformer, Motor, Busbar Overload Standart

04/08/2013 7:40 AM

dear friends

anybody knows, what standart overload at transformer, motor and busbar?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#1

Re: transformer, motor, busbar overload standart

04/08/2013 7:56 AM

Yes, usually the manufacturers go to great extents to make sure their customers know what they have purchased. Generally the standard load is expressed as Full Load Amps (FLA). Different motors have different overload ratings due to start current requirements and possibly other factors.

A transformer overload causes distorted wave shapes and severe heat damage. A busbar overload is generally catastrophic so it could only be for a very short time if at all. But everything has its limits. To give you an understanding about this, consider the following image relating to both overload and underload limits for a computer power supply. Time is a very big factor in the overall consideration.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply Score 1 for Good Answer
Anonymous Poster #1
#2
In reply to #1

Re: transformer, motor, busbar overload standart

04/08/2013 8:41 AM

When i have transformer rating 200 kva, what the setting overload limit in percent of the ratting? could u give me the standart that refers to this?

and also in motor, and busbar

thank u

Reply Off Topic (Score 5)
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: Transformer, Motor, Busbar Overload Standart

04/08/2013 10:59 AM

If you have a transformer rated at 200KVA, then it is overloaded at 200.001KVA. Most people use a standard of 80% of full load as a maximum load just because you have to leave a little room for unexpected events such as start ups of big motors, etc.

A motor, transformer, and busbar are three very different kinds of items. Decisions of how to use them will determine how quickly they fail. The user is generally not the expert on these matters. The manufacturer is responsible for doing the testing on his product. Therefore, the manufacturer is probably going to be the most qualified to answer your question, or they will probably only be in business for a very short time.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Transformer, Motor, Busbar Overload Standart

04/10/2013 9:47 AM

Pl. refer to application guides on transformers, motors & protective relays.

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); electricalexpert65 (1); NotUrOrdinaryJoe (2)

Previous in Forum: Analog Power Factor Meter Connection   Next in Forum: Diversity Factors in Transformer Sizing - Reference Standard?

Advertisement