Selection of Thermal Overload

05/15/2013 3:38 PM

Hi

i have only following specification from my client, and has to buy thermal overload,

0.75 kw, 380 v, 3-phase, 50 Hz, geared induction motor

I=750/(380*1.732*.8(pf)*.8(eff))=1.78*1.25(25%)=2.25 Amp so overload 2-3 amp

i have taken these calculation from internet, practically this overload will be fine?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: selection of thermal overload

05/15/2013 3:41 PM

I think your client needs to do a bit better job in doing their due diligence in selecting who they use as outside contractors

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4
In reply to #1

Re: selection of thermal overload

05/15/2013 4:05 PM

He could be the consultant not the contractor.

Jack - Oh I could tell you stories about consultants.

__________________
jack of all trades
Register to Reply Off Topic (Score 8)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#7
In reply to #4

Re: selection of thermal overload

05/15/2013 8:49 PM

good point

Register to Reply Off Topic (Score 7)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: selection of thermal overload

05/15/2013 3:54 PM

Are you charging your client for your services?

If so, please see #1.

The overload will be fine, till it blows.

Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: selection of thermal overload

05/15/2013 4:03 PM

Best you go back and check the motor's actual and starting current (and other real-world characteristics) also.

Due diligence and all.

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: selection of thermal overload

05/15/2013 4:06 PM

Toy Boat,

Toy Boat,

Toy Boat,

Toy Boat,

Toy Boat,

Toy Boat,

Toy Boat,

Toy Boat,

Is this a homework question or a demonstration of your competence?

Toy Boat,

Toy Boat,

Toy Boat,

Toy Boat.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 6)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: selection of thermal overload

05/15/2013 4:14 PM

In defense of this person who so casually includes "engg" in their name, I can say with certainty that they demonstrate complete incompetence in many fields.

A review of their stimulating historical questions proves this conclusively.

Register to Reply Off Topic (Score 6)
Associate

Join Date: Apr 2011
Posts: 43
#8
In reply to #6

Re: selection of thermal overload

05/15/2013 11:14 PM

Thanks Mr. Guru for ur comments. If u please pin point the questions from where u judged my incompetence. Incompetence can never be judged by questions.

Register to Reply Off Topic (Score 6)
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#9

Re: Selection of Thermal Overload

05/16/2013 9:54 AM

Come again: when and how did thermal overload requirements get translated into overcurrent?!? The last time I looked, those are physically different breakers for different purposes. They look different, and placed different.

The trip points:

one in Celsius

the other in Amperes

How does one gets converted into the other?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #9

Re: Selection of Thermal Overload

05/16/2013 10:50 AM

Thermal overload relays do exactly that. They are current sensing devices pre-calibrated to mimic the thermal damage curves of motor winding insulation based on the amount of current flowing to the motor. That concept goes back about 100 years now. Keep up.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#12
In reply to #10

Re: Selection of Thermal Overload

05/16/2013 12:17 PM

I DO keep up.

Over many years I found myself in agreement with you, and learned a lot of high power and Variable Frequency Drives.

This time I was talking from experience, trying OP to open up. Many motors, I dealt with (in the few and sub KVA range) have a fuselike device attached to the winding, or a bimetallic resettable switch (frequently inadequate quality), singularly for overtemp. sensing, and tripping.

Having a long life in electronics and lower power apps. R&D, mostly, I think you misstepped on this one.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #12

Re: Selection of Thermal Overload

05/16/2013 4:27 PM

Sorry, when posting from my iPad, I don't have access to the "smileys". That should have had one of these... because I was messing with you.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#14
In reply to #13

Re: Selection of Thermal Overload

05/16/2013 4:34 PM

Fine, have a good day.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#15
In reply to #13

Re: Selection of Thermal Overload

05/16/2013 7:08 PM

You know back in my day we didn't have "smileys" but we made do.

;)

__________________
jack of all trades
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#16
In reply to #15

Re: Selection of Thermal Overload

05/16/2013 8:20 PM

But we didn't have internet forums either.

We talked face to face, where winks and nudges were more obvious.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Selection of Thermal Overload

05/16/2013 10:57 AM

Despite the abuse that you may or may not deserve, you need to state your problem a little better. Overload settings MUST by definition be based upon the motor NAMEPLATE FULL LOAD AMPS, not a calculation, because your calculation has to assume facts not in evidence.

However if you GOAL is to pre-select and appropriate RANGE of Overload Relay adjustment because you do not yet HAVE the motor nameplate data, then you have achieved your goal, but "your mileage may vary" as they say in car commercial disclaimers. Motor efficiency and base power factor have a lot to do with the FLA results and with a small adjustment range comes a risk of being off by just an RCH.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Fredski (2); jack of all trades (3); JRaef (4); kazengg (1); leveles (3); lyn (2); redfred (1)