Retraceable Grounding

05/22/2013 5:40 AM

Dear All

Greetings, i have one issue about retraceble grounding, We are constructing a oil & gas plant, i am on client side, We have to make a system for condensate loading for trucks, we have requested to contractor to provide separate retraceable grounding for truck during loading of condensate.

the contractor is saying that all the tanks & loading /unloading pumps are earthed & we don't need to ground the trucks separately.

Is it recommended?

Thanks in advance.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#1

Re: Retraceable grounding

05/22/2013 5:44 AM

Rubber tires makes for static electricity. Find a better contractor.

Reply Score 1 for Good Answer
Anonymous Poster #2
#2

Re: Retraceable grounding

05/22/2013 6:04 AM
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#3

Re: Retraceable Grounding

05/22/2013 11:28 AM

Perhaps you meant "retractable" and not "retraceable".

In any case, yes, the trucks must be bonded to the same bonding system that the delivery system (pumps and piping) are bonded to.

This is often done by the use of retractable bonding jumpers with secure and approved clamps that connect to the trucks. These jumpers are housed in spring tensioned reels that allow the jumpers to rewind on to the reel when not needed so that the jumpers do not lie all over the ground and get damaged.

Why? Because the flow of the product in the delivery piping can cause a static charge to build-up to the point where the potential difference can cause all sorts of electrostatic discharge.

Bonding the whole system together provides a path for that static buil-up to be sucked off before the levels get to the point that a discharge is possible.

The bottom line... the contractor needs to meet the requirements of its customer.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Retraceable Grounding

05/22/2013 3:47 PM

If static discharge could make the condensate go bang then the trucks need to be properly earthed. Relying on metal pumps and hoses is not going to be enough.

If in doubt (or the contractor won't accept this) then consult your local hazardous area inspector for some site specific advice they will have to follow.

__________________
jack of all trades
Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#5

Re: Retraceable Grounding

05/23/2013 12:51 AM

Get a better contractor.

Where I live, fuel delivery trucks, airplanes etc, ALL are grounded before hoses are connected. No exception. Static discharge ignited fumes are nasty.

Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#6

Re: Retraceable Grounding

05/23/2013 3:18 AM

Wrong. If the truck is carrying any sort of store static charge, which it certainly will have, the truck needs to be earth before any off loading/loading occurs. Even if the tanks are earthed.

If the tanks are earthed and the filling hose is earthed, then on contact to the filling nozzle the hose will earth the truck. But, it is always a standard safety procedure to earth the truck before any loading off loading takes place.

Static charges build up to high voltages and a simple spark could ignite any gases present in the air that may combust. It only takes 7kV static charge to cause a spark.

Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); fixitorelse (1); IQ (1); jack of all trades (1); leveles (1); North of 60 (1)

Previous in Forum: AC & DC in 1 Cable Ducting   Next in Forum: 3rd Harmonic Current

Advertisement