Panel rating

06/03/2007 6:23 AM

- How can I rate a main distribution panel serving 3 Sub-main panels. Assuming each Sub-main panel is rated 125 A and have a load of 39.5 KVA.

- With 120/220 Vac, 3ph, 4 wire, 60 Hrz.

Thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Panel rating

06/03/2007 1:35 PM

Both the CEC and the NEC have clear and precise guidelines on how to do load calculations. In the CEC, for example, section 8 contains all of the rules and demand factors that are inputs to the calculations used to determine the minimum size a service.

If it was me, I would do a load calculation for the whole facility, using whatever code is in effect in your jurisdiction, then once the total demand is known, do load calculations for each of the zones covered by the three sub panels and then size their feeds as indicated. The calculations for the three zones should roughly equal the total for the whole building, at least they should if the calculations were valid.

By the way... you must mean "120/208v" as there is no such thing as a 120/220V 3ph 4w system.

Best advice... get a pro.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Active Contributor

Join Date: May 2007
Location: Vermont and Alaska
Posts: 24
Good Answers: 3
#2

Re: Panel rating

06/04/2007 9:15 AM

Is the system a 120/240 (center tap grounded) 4wire DELTA or is it a 120/208 (grounded neutral) WYE?

120/220 4W 3-phase is not an option. The actual voltage is critical to sizing the MDP. Another factor to consider is the characteristic of the load. Are they continuous ( capable of operating more than 3 hours).