Anonymous Poster #1

Selection on LV and MV

08/02/2013 6:24 AM

Dear all,


I have 3 questions..

1. What is the criteria for selecting the voltages between LV and MV (other than availability).How much load can we connect to one particular voltage.I mean generally up to how much kW can we connect to 415 V..or 6.6kV or 11kV?


2.The maximum rating of the motor connected to 415 V is limited to 250 kW.What is the reason..?

3.It is a common practice to select Air circuit breakers for feeders rated above 800 A in Low voltage systems (<1000V).MCCB has ratings upto 1600 A some manufactures provide 3200 A MCCB.Then Why is this limitation..?

Please share the answer if you know...

Regards

Syam.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Selection on LV and MV

08/02/2013 9:51 AM

The short_circuit capacity of low voltage circuit breaker is limited to 45-50 kA The short-circuit impedance of a low voltage transformer is limited to 6-8% since the voltage drop is limited to +/- 5%[up to a receiver terminal]. That means the maximum transformer power could be 2500-3000 kVA.

The locked rotor motor current is 6.5-8 times the rated.

A 250 kw [4 poles] rated current is 450 A[around] and the locked rotor current 3000 A.

Transformer Full Load Current Itrf=2500/sqrt(3)/0.4=3608 A.

If a transformer is full load and a motor will be in locked rotor situation[DOL start or blocked]then will be more than 10% voltage drop at transformer terminal[only] and that will disturb the other receivers as other motors , controls, lighting and other[under voltage].

No such phenomenon happens on 6.6[or 11] kV, since the rated motor current is low and the voltage drop of tens -or even hundred-volts does not disturb 6.6 kV System

__________________
Julius
Reply Score 1 for Good Answer
Anonymous Poster #2
#4
In reply to #1

Re: Selection on LV and MV

08/02/2013 7:39 PM

Good and Interesting answer indeed, Would you elaborate more on how you calculate 10% VD at transformer terminals?

Reply
Anonymous Poster #1
#8
In reply to #1

Re: Selection on LV and MV

08/21/2013 12:57 AM

Thank you for your reply

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Selection on LV and MV

08/02/2013 10:25 AM

Interview questions, or homework?

Where have you looked, so far?

Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3
In reply to #2

Re: Selection on LV and MV

08/02/2013 11:42 AM

It appears to be questions asked to a fresher at his interview which he could not answer, now he wants to get an answer from us it seems.

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#5

Re: Selection on LV and MV

08/03/2013 1:56 AM

1. Total connected load to the system will decide the voltage selection.

2. Answered already in (1) above

3. There is no hard & fast rule as to the provision of an MCCB or an ACB for a given load. Both are circuit breakers and are covered in the same standard (IEC 60947-2). It bis only designer's choice. ACB is maintainable & MCCB is not.

Reply
Anonymous Poster #1
#7
In reply to #5

Re: Selection on LV and MV

08/21/2013 12:53 AM

Thank you for your reply...

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Selection on LV and MV

08/03/2013 2:02 AM

Anonymous #1

It is very simply. The transformer rated current it is 3608 A [apparent] =3067-j1901 [p.f.=0.85].

Motor starting current =900-j2862 A.[p.f.=0.3]. Total current 3967+j4762 A.

Transformer impedance[8% for 2500 kVA,400 V]ztrf=0.00512 ohm. xtrf/rtrf=7.

xtrf=ztrf/sqrt(1+1/49)=0.0050685. rtrf=0.0007241.

DV=sqrt(3)*(3967*0.0007241+4762*0.0050685)=46.8 V[11.7%].

__________________
Julius
Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); Anonymous Poster (3); electricalexpert65 (1); lyn (1); V.I.Abraham (1)