Paralleling of transformers

06/03/2007 10:36 PM

Dear Sir,

Could any one please explain the effects of paralleling of different impedence transformers with same vector group and size (kVA)?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#1

Re: Paralleling of transformers

06/04/2007 12:32 AM

You're no doubt going to get a vast amount of neat formulas to explain exactly how this works. Electrical calculations are pretty much straight mathematics, meaning, what you draw on paper you can generally count on to actually measure when built and functioning.

Here's a boiled down common sense characteristic. If the transformers were EXACTLY the same, then the current would divide evenly or each one could contribute it's full name-plate capacity... ( 2 ) 10 kva transformers would indeed provide 20 kva.

In reality, the impedance of LIKE transformers but from different manufacturers, would be different and ( 2 ) 10 kva transformers would NOT be "worth" 20 kva, rather, all paralleled transformers will be de-rated to the actual capacity of the weakest transformer. Example, the weakest transformer in a bank of paralled 8 kva, 9 kva and 10 kva would NOT deliver 27 kva or even 24 kva, it'll be less. The weakest link ( highest impedance ), gets the highest voltage drop therefor has an "unfair burden" of heat dissipation. The DC resistance of the core copper, the number of actual transformer turns, the number and thickness of the lamanations and the physical stature or ability to shed heat, ALL figure in a transformer's actual capacity.

Same concept as buying matching belts for pulleys or matching power transistors for an audio amplifier.

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#2

Re: Paralleling of transformers

06/04/2007 3:20 AM

The different Z of Transformers will be loaded unevenly if it is paralled.Due to this uneven current, heat devoloped on the winding is more and the class of insulation to be with stand.Also the harmonics will be more at one transformer and it will be less at another transformer.After parallaling properly, this will be normalised subject to the above.It is not danger if you follow the condition for paralleling of Transformers.Practically many distribution transformer were paralled by electricity board and functioning normally with differant impedance.

Register to Reply
Power-User

Join Date: Mar 2007
Location: Northeast Pennsylvania, USA
Posts: 173
#3
In reply to #2

Re: Paralleling of transformers

06/04/2007 10:45 PM

I agree with your "diifferent Z" that leads to different loading, my point exactly. Different harmonics ? I'd think the harmonics are the same unless we're talking about audio transformers. And...you said the power companies do this all the time, yes, I know that for sure, I worked for an electric utility for 11 years. They can safely parallel transformers because they use MATCHED transformers. Once again, I assure you, can NOT deliver the sum total kva of unmatched transformers in parallel because the weakest transformer will overheat.

__________________
Unless you're the lead dog on the sled, the view is always the same....
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Feb 2007
Location: Next to the Prime Merridian (51°29'34.50"N 0°13'32.85"W)
Posts: 780
Good Answers: 1
#6
In reply to #3

Re: Paralleling of transformers

06/05/2007 6:20 AM

Hi there,

I don't know which one of you to address with this issue because a few you confusing me.

My Q is:

What role harmonics has here?

Why would anyone try to paralell up unidentical transformers on the secondary side?

As I can see it thre's no problem on the primary side, as long as it is connected to the grid, but it is definately a concern on the secondary side because of the one with higher dc impedance (weaker trf) would work into the one with the lower dc impedance(stronger trf) due to a phase shift difference between them, however small it maybe.

Does this make sense?

__________________
Making mistake is part of learning.
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 178
Good Answers: 3
#4

Re: Paralleling of transformers

06/04/2007 11:13 PM

Power companies do it frequently in power sub stations but the primaries are (generally) fed from different sources. The main problem with these applications is voltage mismatch (and other phase angle displacements) that cause circulating currents to flow and tend to heat the transformers. Generally they are paralleled only for short durations (Via Bus tie breakers) in order to maintain continuous service to the customers during the transfer of loads.

Register to Reply
Anonymous Poster
#5

Re: Paralleling of transformers

06/05/2007 2:44 AM

Friends,

With all said and done is it impossible to overcome these obstacles of impedence mis-match? If I have three sources of power and make some kind of redundant power arrangement this idea/trick will be very useful. What is the way out? Other than using UPS/Inverters.

R. GANAPATHI RAO

INDIA.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#7

Re: Paralleling of transformers

06/20/2007 7:18 AM

See following Posts: 1.} Combining portable generator output <http://globalspec.ip09.com/rd/9z1z4o4akgbccedogn3ca55c4ivu29tpnsnh7vgo1dg> (Electrical Engineering) 2.) Haajee Power-User Join Date: Feb 2006 Location: Pakistan: 33.2N; 72.16 E Posts: 163 #2 [New Comment] Re: 05/10/2007 6:39 AM In parallel you should have exactly balanced O/P Voltage. If a slight difference is there sharing will be accordingly in: Imbalanced Load for a Double-Wound Transformer <http://globalspec.ip09.com/rd/9z1z2tkf2d9e2c2u1se3iu91si9bqn08lsrbmk4pue8> (Electrical Engineering) 3.) Davegur Active Contributor Join Date: Mar 2007 Posts: 12 #1 Re: Can I connect two 12v rails on a PC power supply? 04/27/2007 1:16 PM Yes, provided the 12volt rails have a over-crrent protection charecteristic, otherwise one may supply the majority of the output and overheat. and more ... in: http://cr4.globalspec.com/thread/7368/Can-I-connect-two-12v-rails-on-a-PC-power-supply Can I connect two 12v rails on a PC power supply? <http://cr4.globalspec.com/thread/7368/Can-I-connect-two-12v-rails-on-a-PC-power-supply> and more ...

Register to Reply
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); G.Swaminathan (1); Haajee (1); Isti80 (1); Snakers (1); Sniccus (2)

Previous in Forum: faceplate starter   Next in Forum: Impedence
You might be interested in: KVA Meters, Transformers, Electronic Transformers

Advertisement