Buchholz Relay/Conservator

08/30/2013 9:26 AM

Hi colleagues :)

I was making a research about the Buchholz relay in transformers. In an older post in this forum I have seen the following sentence: "The hermetically sealed transformer is the transformer without the conservator tank." In another website I found as well that "a hermetically sealed transformer is more reliable than a conservator type transformer".

But I have a technical specification from a manufacturer saying that his transformer is hermetically sealed and in the drawings I have notice that it has a conservator. Is it possible?

Another question... when having Buchholz relay, conservator is a must. But, having conservator, is Buchholz relay a must?

Thank you for your time and your patient! :)

Jorge

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Buchholz Relay /Conservator

08/30/2013 10:53 AM

"Hermetically sealed" means isolated from the outside atmosphere, it's sealed so that nothing escapes or gets in. But if you have a sealed container and the fluids inside expand and contract with temperature changes, you need a way to accommodate those changes. You can put inert gas above the fluid, you can put a pillow/bladder filled with an inert gas riding on the fluid, or you can have a tank into which the fluid can flow as it expands aka the conservator.

Separately from the above, you need to monitor the level of the fluid, its rate of change, and the amount of gas that may be generated; plus you have to distinguish between normal and abnormal changes. That's what the Bucholz relay does, it ignores operational changes in the level, alarms on increased internal gas production, and trips on rapid changes in fluid pressure/flow, usually into the conservator.

Whether you have a Bucholz relay, or any other form of protective relaying, depends upon the value/importance of the asset you're protecting. The larger the transformer the more likely it is to have a Bulcholz, but where the cutoff is is a function of the operating/relaying philosophy of the particular utility operating company. So you may find transformers with a conservator but no Bucholz, but not the other way around.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Jul 2013
Posts: 15
#3
In reply to #1

Re: Buchholz Relay /Conservator

09/02/2013 3:20 AM

Thanks a lot RAMConsult, is the answer I was looking for! :)

Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#2

Re: Buchholz Relay/Conservator

09/01/2013 1:27 AM

Exactly what information are you looking for?

Google it!

http://www.electrical4u.com/buchholz-relay-in-transformer-buchholz-relay-operation-and-principle/

Construction of Buchholz Relay

Buchholz Relay in transformer is an oil container housed the connecting pipe from main tank to conservator tank. It has mainly two elements. The upper element consists of a float. The float is attached to a hinge in such a way that it can move up and down depending upon the oil level in theBuchholz Relay Container. One mercury switch is fixed on the float. The alignment of mercury switch hence depends upon the position of the float.

The lower element consists of a baffle plate and mercury switch. This plate is fitted on a hinge just in front of the inlet (main tank side ) of Buchholz Relay in transformerin such a way that when oil enters in the relay from that inlet in high pressure the alignment of the baffle plate along with the mercury switch attached to it, will change.

In addition to these main elements a Buchholz Relayhas gas release pockets on top. The electrical leads from both mercury switches are taken out through a molded terminal block.

Buchholz Relay principle

The Buchholz Relay working principle of is very simple. Buchholz Relay function is based on very simple mechanical phenomenon. It is mechanically actuated. Whenever there will be a minor internal fault in the transformer such as an insulation faults between turns, break down of core of transformer, core heating, thetransformer insulating oil will be decomposed in different hydrocarbon gases, CO2 and CO. The gases produced due to decomposition oftransformer insulating oil will accumulate in the upper part the Buchholz Container which causes fall of oil level in it.

Fall of oil level means lowering the position of float and thereby tilting the mercury switch. The contacts of this mercury switch are closed and an alarm circuit energized. Sometime due to oil leakage on the main tank air bubbles may be accumulated in the upper part the Buchholz Container which may also cause fall of oil level in it and alarm circuit will be energized. By collecting the accumulated gases from the gas release pockets on the top of the relay and by analyzing them one can predict the type of fault in the transformer.

More severe types of faults, such as short circuit between phases or to earth and faults in the tap changing equipment, are accompanied by a surge of oil which strikes the baffle plate and causes the mercury switch of the lower element to close. This switch energized the trip circuit of the Circuit Breakers associated with the transformer and immediately isolate the faulty transformer from the rest of the electrical power system by inter tripping the Circuit Breakers associated with both LV and HV sides of the transformer. This is how Buchholz Relay functions.

Buchholz Relay Operation - Certain Precaution

The Buchholz Relay operation may be actuated without any fault in the transformer. For instance, when oil is added to a transformer, air may get in together with oil, accumulated under the relay cover and thus cause a false Buchholz Relay operation.That is why mechanical lock is provided in that relay so that one can lock the movement of mercury switches when oil is topping up in the transformer. This mechanical locking also helps to prevent unnecessary movement of breakable glass bulb of mercury switches during transportation of the Buchholz Relays.

The lower float may also falsely operate if the oil velocity in the connection pipe through, not due to internal fault, is sufficient to trip over the float. This can occurs in the event of external short circuit when over currents flowing through the winding cause overheated the copper and the oil and cause the oil to expand.

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Active Contributor

Join Date: Jul 2013
Posts: 15
#4
In reply to #2

Re: Buchholz Relay/Conservator

09/02/2013 3:21 AM

Thanks Macgyver!

I had seen that website, but it didn´t explain me what I was looking for! But now its perfeclty clear! Anyhow thanks a lot! :)

Register to Reply
Participant

Join Date: Sep 2015
Posts: 1
#5

Re: Buchholz Relay/Conservator

09/23/2015 10:58 AM

If you still need to find a solution check it here

http://911electronic.com/

Register to Reply
Participant

Join Date: Feb 2018
Posts: 1
#6

Re: Buchholz Relay/Conservator

02/14/2018 8:20 AM

I think most of the information is said. Short summary is that there is no need to have a Buchholz relay for a hermetically sealed transformer. If you have a hermetically sealed transformer a all-in-one device should be used. This device/relay will be assembled on the tank cover of the transformer and measures oil level, gas accumulation, oil temperature and internal pressure.

I´d like to add some information that there is a Buchholz relay with a separated switching system from the oil circuit. This prevents any issues coming from electrical fault by the contact. The float movement will be transfered by a magnet which is inside the float. The floats moving along a brass pipe where the reed-switches are in.

I really hope this information helps you out a little. A few years age when I started to work in this business, I had the same questions and it took a while to understand

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electronican (1); jorge1 (2); Original_Macgyver (1); RAMConsult (1); Sebastian Müller (1)

Previous in Forum: Combining Two Neutrals in a Single Generator   Next in Forum: POWERWIZARD 1.0

Advertisement