Anonymous Poster #1

VAR/PF Swing

09/09/2013 10:18 PM

Dear every body,

I have a problem for a long time ago and appear back till now. Our generator output VAR/PF swing. Our system in BUS # 3 is two generators parallel and grid (two three winding transformers). The generator is Brush-less Parallel" type (see Electric machinery manufacture).

So far, we already monitoring the control AVR (input/output response) of two generators, The result are GOOD. But we found something made trouble. One of generator first made VAR/PF swing. till we decided to check (generator suspect) : all diode and fuses, rotor-stator exciter, main rotor field, stator PMG.

The of all diodes and fuses result are GOOD.

Insulation resistance rotor-stator exciter, main rotor field and stator PMG are GOOD.

We're not check winding resistance of them.

The QUESTION:

- If something problem with the rotor exciter winding (aren't balance), What is effect to the output generator / could be make VAR/PF swing?.

regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#1

Re: VAR/PF swing.

09/09/2013 10:45 PM

Swing is very vague statement.

Does power factor hunt continuously?

Or it suddenly turns capacitive on one and inductive on another?

Does this happens when parallel with Grid or in Island mode?

What are the ratings?

Above needs to be clarify. Each has different reason and solution - so that we can comment on possible cause and solution.

I

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: VAR/PF Swing

09/09/2013 11:11 PM

In addition to the above questions, please provide information on what was being done when the problem reappeared, things like: adjusting load or voltage, synchronizing, after maintenance, repair, forced outage, etc.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#3

Re: VAR/PF Swing

09/11/2013 12:50 AM

Other questions need to be answered to get answers, what is the prime mover, is the input power connected in any way like a common steam boiler, what are the relative sizes, is there a paralleling circuit to prevent the swings?

Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#4
In reply to #3

Re: VAR/PF Swing

09/11/2013 1:04 AM

Prime mover comes in to discussion if the swing was in kW. Here Anonymous Poster # 1 has problem of VAR swing and resultant change in PF.

Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5

Re: VAR/PF Swing

09/11/2013 8:47 AM

Any problem with the exciter and /or the AVR, or the Load Sharing section of the controls will have an effect on the output. Since this is running in parallel, then also with the VAR and PF

Remember that the PF is dependent on the load and , unless the load is varying and creating a sudden demand for VAR, the production of VAR from all the Gen-sets in parallel, will be the same. Then if One gen-set seems to have a swing to produce more VAR, the others will have a swing to produce less VAR (and will see a better PF).

please check and answer the questions allready put to you by other contributors...

Reply