Abnormal sound on busduct

06/05/2007 8:11 AM

We have conneted a 1000kva Transformer secondry (415volt), with 2000amps Air circuit Breaker through the Aluminium Busduct which is supported on the insulator. Some time the abnormal sound created in the duct area.This sound is automatically stopped after 4 hours duration.During this period load current is between 550amps and 1050amps only.We have verified all the tightness in the busduct area from the secondry of transformer to the ACB end.Still this proublem is not solved even after made the tightnees.What are all the reason possible for this sound within the duct? and How to reduce the sound? Is there is any possibilities for insulation weeknees on the insulator?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#1

Re: Abnormal sound on bus-duct

06/05/2007 10:15 AM

Without hearing the sound, It could be a number of things

Electrical sounds (small explosions) would be caused by arcing which could be a result of

  • oxidization on the aluminum,
  • loose connectors,
  • Connections with resistive joints or insulator breakdown,
  • Bolts that come too close to each other or the duct cover
  • poor tining finish
  • Dent in the duct

Here is a few installation check points

http://ecmweb.com/mag/electric_ensuring_good_bus/

Mechanical sounds, regular bangs such as the pluming noises in a hot water line.

Mechanical sounds are usually caused by heating and expansion which cause movements of the conductors or the ducts. Even external heating not related to the power or load can cause this, such as the sun coming in a window onto the duct at a certain time, or a heat source below the duct. An Infra red detector would be helpful in finding the heat source

If this is a long duct (>20M) you may think of installing a flexible bus-duct connector such as on page 4 of this link to prevent thermal expansion noises

http://library.abb.com/GLOBAL/SCOT/SCOT209.nsf/VerityDisplay/21623CC783BB59E8C2256DD000264696/$File/MDY_Brochure_English.pdf

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#3
In reply to #1

Re: Abnormal sound on bus-duct

06/06/2007 7:51 AM

Sir,

you have given the valid points to solve the proublem.We will attend this points during shutdown period.Thank you for your answer.Any doubt we will raise again.

Register to Reply
Guru

Join Date: Dec 2005
Location: Queensland Coalfields Australia.
Posts: 697
Good Answers: 11
#2

Re: Abnormal sound on busduct

06/06/2007 1:04 AM

Does the noise recurr each day? If so it is likely to be due to the ripple control frequency the supply authorities use for load control. It is typically about 1200hz.

Register to Reply
Anonymous Poster
#4

Re: Abnormal sound on busduct

06/06/2007 8:51 AM

Aluminium is much less denser than copper and it transmits sound from vibration to greater extent.

The noise could be something as simple as enhanced 50 Hz hum or possibly harmonics in the neutral assuming it s 415 v 4 wire - is there a lot of fluoresecent lighting the load?

On a more postive note if it was something more serious I suspect there would be other signs - smoke or smell, by now.

Sorry but unless you can post a sample of the noise on the forum, its difficult comment further.

Register to Reply
Guru

Join Date: Sep 2006
Posts: 4513
Good Answers: 88
#5

Re: Abnormal sound on busduct

06/07/2007 10:56 AM

Would you describe the nature of the sound in some detail? For example, is it a humming sound or more like (white or pink) noise? Popping sounds? Please describe. These all have different sources and knowing the nature of the sound will go a long way in determining its source.

Register to Reply
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#6
In reply to #5

Re: Abnormal sound on busduct

06/07/2007 11:52 PM

Sir

It is humming sound only.Give me reply please.

Register to Reply
Guru

Join Date: Sep 2006
Posts: 4513
Good Answers: 88
#7
In reply to #6

Re: Abnormal sound on busduct

06/09/2007 12:13 PM

This is a hunch only, but given the magnitude of the current flowing through the conductors, and if a conductor and its return path are in reasonably close proximity, the current will produce a substantial A.C. magnetic field. This field can cause the conductors to oscillate at points between their mounting points.

As an experiment, you could install additional insulated mounts between the existing ones to dampen the oscillations. Or, if it is convenient, move the conductors farther apart.

Alternatively, you could wrap the conductors in a sound-dampening, insulating material, such as Sorbathane (a trade name for a non-porous, ultra-soft polyurethane) sheet to minimize vibration. McMaster Carr is one supplier of Sorbathane.

A strip of Sorbathane along the length of the bus duct will also dampen vibration, as will a strip of lead sheet.

The foregoing assumes that it is the conductors that are vibrating, producing the humming sound. If you can record this sound to a file, there are a number of inexpensive (and free) spectrum analyzer programs available which can reveal the hum frequency and harmonics. Chances are that if the source of the hum is the A.C. magnetic field surrounding the conductors, the primary frequency will be some harmonic of the mains frequency in combination with the natural resonant frequency of the bus duct.

Please understand that as I can't be there to actually see your installation, this is mere speculation on my part. On the other hand, experimenting with dampening materials would be fairly inexpensive, and could reveal enough information about your hum problem to lead to a resolution.

If you try this, please contact me (or respond to this thread) to let us know how it goes.

-e

Register to Reply
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#8
In reply to #7

Re: Abnormal sound on busduct

06/09/2007 1:23 PM

Surely i will give reply after taking experiment analysis.More over i can operate at full load from28th of this month, since this is the acadamic year opening date of our university.Thank you for your reply.

Register to Reply
Register to Reply 8 comments