hello sirs

anyone can give me some guidance about generator rotor resistance.we have ansaldo energia 170Mva generator.its rotor resistance value at 95°c is 0.2°Ohm(200mohm) as per data sheet.but during resistance measuring we get it only 2.31mohm with digital low resistance ohm meter(Magger make).

so please give me some hint how I get proper value. why I get only 2.31m ohm inspite of 200m ohm.

__________________
Curiosity made genius
Register to Reply
Pathfinder Tags: generator rotor resistance
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Feb 2013
Location: Australia
Posts: 26
Good Answers: 2
#1

Re: Generator Rotor Resistance

11/24/2013 1:50 AM

First thing I would like to clarify, I am presuming that you have requested the information from the manufacturer of your machine, and they have provided the correct information.

If the information is correct, then I would suggest that there possibly could be 2 short circuits on the insulation of the rotor windings.