I am having issues at a customer's well site deep in Adirondack Mountains, upstate NY. Customer has 230VAC 1-phase utility feed, and a 230VAC 3-phase backup generator, plus an automatic transfer switch.
There are two ACS550s, off the common 230VAC output of the ATS. Each one is wired through a disconnect and a line reactor prior to the VFD. Right now, the pumps operate in parallel, each having an analog signal reference from PLC. Both pumps are sent the same reference value.
When utility power goes down (which happens quite frequently in that part of the world), both VFDs and PLC lose power for about 15 seconds before generator spins up and ATS switches to generator. Everything comes back up just fine, and pumps restart at same speed as before switchover. No issues there.
When utility power restores, ATS switches back over, which drops the #2 or V-input phase to both drives at the ATS, so now the V-inputs of the drives are essentially directly connected with two line reactors between them.
One drive starts up and runs okay, the other tends to go into severe surging, almost as if the drive is being limited, then recovering, then going back into limiting, etc.
Also, and this may be more an issue with water lines and flowmeter, the two pumps appear to be delivering only 1/10th the flowrate as before the switchover back to utility power.
Both drives, per ABB, are derated 50% for single phase duty.
ABB tech support is insisting the problem is with PLC changing reference to VFDs; I have been unable to uncover any problem with PLC, reference signal to drive is steady at 100% once power is restored to PLC.
They also don't think the problem is related to any coupling between the V-input phases when disconnected from a power source, but I'm not convinced.
Any of you folks have any relevant experience that might help us resolve this issue? I'd appreciate any advice on what to check, what to try.