Mixed Voltages in Industrial Junction Box.

11/27/2013 1:16 PM

Apart from good practice, common sense and a desire to make things safer is there any UK legislation that would prevent you from constructing a junction box with 460VAC immediately beside 110VDC, signals to open and close HV switchgear, generator CTs, and all of the usual stuff all mixed up together. Is there a standard that says this cannot be done. Is there a standard that says there must be segregation and that there must be nice plastic covers shrouding the terminals sporting useful advice like Danger 460V. Did I mention the junction box was metal.

This is a legacy box rather than a new design. I really need a BS or IEC standard to quote to condemn it.

Its absolute tat and dangerous but its there and needs to be condemned.

Register to Reply
Pathfinder Tags: mixed voltages
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: Mixed Voltages in Industrial Junction Box.

11/27/2013 1:23 PM

I think your first sentence is good enough to condemn it.
If some customer or your boss wants chapter and verse, make sure you research it on their time!
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Mixed Voltages in Industrial Junction Box.

11/27/2013 1:42 PM

The only standard that governs mixed voltages in the same raceway. Is that the insulation on the wires must be rated for the highest voltage. So if one of the lower voltage conductors has insulation not rated for 460vac. Then there is reason for you to condemn it.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2011
Posts: 131
Good Answers: 5
#3
In reply to #2

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 12:00 AM

Is it 460 V ac or Basic Impulse Level (BIL) ? As far as I know BIL for 460 V system is 600 V as per standard in US.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 12:57 AM

Junction box or control panel/distribution board?

Photo?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#5

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 2:30 AM

Its an old junction box just over 800mm x 800mm made of mild steel plate and is absolutely packed. The machine it is fixed to is being refurbished and the owner is keen to rebuild the JB as it is. My own thoughts are that its madness and will be featured in an accident report. There is a gap between what we both believe to be a safe installation.

Sadly all of the cables are rated sufficient for the voltages contained within the panel. My recommendation is to condemn it. I just can't believe there is no standard to cover it - even things like shrouding and labelling.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#7
In reply to #5

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 2:57 AM

Sounds like a control panel.

If the wiring is in a dilapidated state then you can condemn the wiring and have it rewired. If on top of the dilapidation the enclosure is so jam packed with (most likely) add-ons that it was never intended to accommodate then you may have a case for installing an additional outboard junction box to allow structured wiring practices to be reinstated.

If it is really jam packed it may well be thermally overloaded as well which gives you another avenue for a replacement or augmentation justification.

Do you have the original drawings?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#8
In reply to #7

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 6:44 AM

Its absolutely a junction box. There are 7 vertical rails of Klippon type teminals of varying types. It has a lid on and needs tools to get into it.

The safety culture we follow today the younger guys know if it hasn't got a shroud on it chances are its safe. Similarly they also know that you don't mix up voltages and a random 460V 2 phases next to 110VDC with a battery on the end of it.

It meets all of the cable voltages and creepage.

The older ones know to expect rubbish so are pleasantly surprised when we see a new modern panel.

Still no standards though?

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#10
In reply to #8

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 8:32 AM
__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#6

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 2:52 AM

A penny pinching owner, more concerned with saving a few $ rather than safety and ease of servicing?

Who'd have thought it?


If you really want to do it, show him the cost of adding a second box to allow it to be tided up a bit and point out the maintenance savings of having it clearly labelled and spread out.

Point out it will probably take less time to improve the layout.
If he still wants to just rebuild it... let him get on with it!

Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 8:17 AM

We're getting into the realm of acceptable installation practices and risk mitigation...

Too many beers now to continue blithering.

To be continued....

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#11

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 12:16 PM

If this was an issue in a Canadian jurisdiction, the content of rule 12-3030 would be used to fail this installation... perhaps the BS that Mr. Slack always mentions has a similar requirement.

12-3030 Conductors in boxes, cabinets, or fittings

(1) Conductors that are connected to different power or distribution transformers or other different sources of voltage shall not be installed in the same box, cabinet, or fitting unless

(a) a barrier of sheet steel not less than 1.3 mm thick or a flame-retardant non-metallic insulating material not less than 1.6 mm in thickness is used to divide the space into separate compartments for the conductors of each system;

(b) the conductors are used for the supply and/or control of remote devices and are insulated for at least the same voltage as that of the circuit having the highest voltage and none of the conductors of the circuits of lower voltages is directly connected to a lighting branch circuit; or

(c) the conductors are used for the supply of a double-throw switch in an emergency lighting system.

(2) Where a barrier is used, it shall be fastened rigidly to the box, cabinet, or fitting, or a device assuring positive separation of the conductors shall be used.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#12
In reply to #11

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 12:28 PM

Like the Canadian code Mr Slacks publication contains a similar section regarding segregation of voltages. Unfortunately the UK regs also have part 1 110.2 which specifically excludes various installations - part v being mobile and fixed offshore installations.

Hopefully this issue will get no further than a winge here and will not result in a health and safety enquiry.

Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#13

Re: Mixed Voltages in Industrial Junction Box.

11/28/2013 2:57 PM

If the junction box is used for intrinsically safe wiring used for hazardous areas, then ANSI/ISA-RP12.06.01-2003, Recommended Practice for Wiring Methods for Hazardous (Classified) Areas, Part 1: Intrinsic Safety, requires separation distances and separation barriers.

504.30 Separation of Intrinsically Safe Conductors.

(A) From Non intrinsically Safe Circuit Conductors.

(1) Open wiring. Conductors and cables of intrinsically safe circuits not in raceways or cable trays shall be separated at least 50 mm (2 in.) and secured from conductors and cables of any non intrinsically safe circuits.

(2) In raceways, cable trays, and cables. Conductors of intrinsically safe circuits shall not be placed in any raceway, cable tray, or cable with conductors of any non intrinsically safe circuit.

Exception No. 1: Where conductors of intrinsically safe circuits are separated fromconductors of nonintrinsically safe circuits by a distance of at least 50 mm (2 in.) and secured, or by a grounded metal partition or an approved insulating partition.

(3) Within enclosures.

(a) Conductors of intrinsically safe circuits shall be separated at least 50 mm (2 in.) from conductors of any nonintrinsically safe circuits or as specified in 504.30(A)(2).

I'm sure the standards over the pond reflect similar restrictions, but I don't have those documents.

Register to Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#14

Re: Mixed Voltages in Industrial Junction Box.

12/05/2013 1:26 PM

If you adhere to the local code, you should not regenerate the same condition you found. Any electrical update to the machine should be upgraded to the most recent code. I would not perform any upgrade without doing so!

Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!