Flow Control Valve Operating Mechanism in Boiler

12/06/2013 12:58 AM

Currently i am working on a small boiler, i am controlling Flow control valve externally with respect to temperature. I have calibrated it for 4~20mA signal. but the issue is i want to make it fully open during pre & post purging. I am using Honeywell RM7879A burner controller. Do i need to use some interlock in this controller for FCV signal or i can make some other logic in temperature control unit to fully open FCV during pre & post purging?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Flow Control Valve Operating Mechanism in Boiler

12/06/2013 9:54 AM

Think the easiest way would be to switch over to a constant 20mA source to fully open the FCV. Can you post a link to the burner controller manual? Google didn't help.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#2

Re: Flow Control Valve Operating Mechanism in Boiler

12/06/2013 10:41 AM

Honeywell's site doesn't show RM7879A, is this one of the Delphi's? Is this 'Flow control valve' the air damper (I don't know what else it would be, surely you're not opening the fuel valve during purge.)? The controller must include a start-up/purge process, with associated inputs/outputs - what does the manual say?

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Dec 2011
Posts: 67
#3

Re: Flow Control Valve Operating Mechanism in Boiler

12/07/2013 7:41 AM

https://www.google.com.pk/url?sa=t&rct=j&q=&esrc=s&source=web&cd=1&cad=rja&ved=0CDcQFjAA&url=http%3A%2F%2Fproducts.ecc.emea.honeywell.com%2Feurope%2Fpdf%2Fen-rm7897ac-primary-instructionsheet-66-1151-07-nl05r0812.pdf&ei=BhejUrTtMKqR5ASRmoDQBA&usg=AFQjCNEF540jckOwIq5dr__JIC68qKFqcA&bvm=bv.57752919,d.bGE

Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4
In reply to #3

Re: Flow Control Valve Operating Mechanism in Boiler

12/08/2013 3:21 PM

OK, I see you had a couple of digits transposed in your original post. This seems to be a fairly simple controller intended for use on a single-stage (on-off, non modulating) burner. The only output I see that is 'on' during the pre- and post-purge is the burner/fan contact, which is, of course, also 'on' during the firing. While it might be possible to invert and/or 'and' some of the other outputs to achieve your objective, you haven't provided a complete description of your system and what you are trying to accomplish. This may not be the best controller for your application.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#5

Re: Flow Control Valve Operating Mechanism in Boiler

12/08/2013 5:46 PM

If you are modulating the combustion air with a damper driven by an electric actuator, one technique is to close a contact during the pre or post purge cycle which drives the electric actuator to its full open position, as shown in the diagram for the Honeywell series 72xx Modutrol electric actuator with a 4-20mA input, (document 63-2640-08)


The issue, as bigg has pointed out, is that this particular flame safety controller has no separate 'purge' output and the burner motor output is on for more than just the purge cycles.

Register to Reply
Commentator

Join Date: Jan 2006
Location: Western flank of the Pennines in Lancashire England
Posts: 93
Good Answers: 8
#6

Re: Flow Control Valve Operating Mechanism in Boiler

12/11/2013 4:07 PM

The box you are using is not normally suitable for this application.

Questions relevant to the OP.

  1. Define small boiler particularly peak firing rate. The rules change depending upon the firing rate.
  2. Where are you operating? The rules vary with the location. Why are you trying to re-invent the wheel (burner).
  3. Why not buy a burner from a reputable burner manufacturer supplying your area? You can then be confident that it is going to comply with local regulations and keep your insurance company happy.
Register to Reply
Register to Reply 6 comments