Running 4 Generator Without NGR

01/18/2014 2:57 AM

Dear expert

I have problem with NGR we have 5 Generator (13,8KV,14,5 MW,60Hz) (Y connection) and each generator using NGR. now currently our 2 NGR are not available and we want to running 4 generator parallel and 2 generator without NGR,but we've made residual Ground over current protection as NGR replacement, please advice if there is any concern on protection side if we running with 4 generator parallel?

thank you for your suggest

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Running 4 generator without NGR

01/18/2014 8:15 AM

Dear Anonymous Poster,

Even when all the four NGRs are available, it is general practice to ground only one generator neutral. There should not be any problem, even if you ground only one generator neutral (normally, the neutral of the largest capacity generator), with all other neutrals kept unearthed. Still, the system can be said to be resistance grounded.

And, I am surprised how residual ground over current protection can be a replacement for failed NGRs. The objectives are entirely different.

If you are still worried, you may opt for bus earthing, with a zig-zag earthing transformer, keeping all the generator neutrals floating.

Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#2

Re: Running 4 generator without NGR

01/18/2014 9:18 AM

Earthing via NGR or solid earthing of 3 phase alternator is required:

1. To set reference for Phase Voltage with respect to earth.

2. For safety of Operators and other equipment. Safety of Human - In absence of ngr or solid earth, if any phase of machine develops earth fault - the entire frame of machine shall be at phase voltage. Which can be dangerous if operator touches the frame. Hence in your case NGR is required when the DG Set is running in Island mode.

Once the DG is parallel with other DG Set which has its neutral earthed - above risk is not there.

Safety of equipment -

1. Neutral Voltage will be at phase voltage due to resistance of NGR in earth fault circuit if any one phase develops earth fault - without NGR or Solid earthing - circulating current is Zero in earth circuit and E/F relay will not operate and isolate the fault. In this case because of the earth is at voltage of faulty phase - other phases are subjected to phase to phase voltage and insulation of old machine can fail to earth at weak point - Resulting in phase to phase fault.

2. Since probability of Phase to Earth Fault is many more that Phase to Phase, to avoid damage to equipment at location of earth fault the fault energy is limited to low value but sufficient to be sensed by a protection relay.

Hence NGR is must for all DG Sets for safe running of DG Set before its breaker is closed (synchronized) on 13.8kV system having neutral earth system.

Once the DG CB is closed as above - require only one of several DG to have NGR.

Regarding multiple NGRs (as in your system), please note that if with one NGR Earth Fault Current is I, it will be 4 x I with 4 DG Sets in parallel, each having its neutral earthed through NGR. IN SUCH SYSTEM IT WILL BE DIFFICULT TO ACHIEVE PROPER DISCRIMINATION BETWEEN VARIOUS CBs IN EARTH FAULT CIRCUIT UNLESS THE RELAY SETTINGS ARE REVISED WITH CHANGE IN NUMBER OF DG SETS ON LINE.

Summary:

1. Have NGR in all neutrals for safety before their respective CBs are closed on system having at least one NGR.

2. Have only one NGR closed for multiple sets synchronized on a Bus.

3. Value of Resistance of NGR of all DG Sets (or source) shall be same so that earth fault current does not vary to ensure simple settings of protection relays and discrimination.

Reply Score 1 for Good Answer
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#3
In reply to #2

Re: Running 4 generator without NGR

01/28/2014 3:29 AM

Nicely explained.Thanks for the value addition....

__________________
"Know something about everything and everything about something"
Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#4
In reply to #3

Re: Running 4 generator without NGR

01/28/2014 5:27 AM

Thanks.....

Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); giri (1); powersolutionsFBD (2)

Previous in Forum: Reliability of Small Uninteruptable Power Supplies?   Next in Forum: Surge Arrester

Advertisement