Formulas for Voltage Drop of Motors (Starting & Normal)

01/21/2014 5:54 AM

Hi All,

I have seen two formulas in Nema ICS-14 (Application Guide for Electric Fire Pump Controllers) section 2.3 which are :

Percent voltage drop during motor running : (ZxMFLAx1.15xVLxSqrt(3))/(Transformer size in KVA x1000) Percent voltage drop during motor starting:(ZxMFLAx6xVLxSqrt(3))/(Transformer size in KVA x1000)

I AM NOT ABLE TO TRACK THE CODE REFERENCES OF THE ABOVE FORMULAS, AND IF THEY APPLY TO OTHER MOTORS (OTHER THAN FIRE PUMP)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Formulas for Voltage Drop of Motors (Starting & Normal)

01/21/2014 8:20 AM

Have you asked the NEMA?


NEMA - National Electrical Manufacturers Association

Why would they not apply to other motors?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Formulas for Voltage Drop of Motors (Starting & Normal)

01/21/2014 3:04 PM
Register to Reply
Member

Join Date: Jan 2014
Posts: 8
#3
In reply to #2

Re: Formulas for Voltage Drop of Motors (Starting & Normal)

01/22/2014 5:24 AM

I have sent query to Nema but still with no reply

The above link for other thread didnt conclude with an answer to this thread

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Formulas for Voltage Drop of Motors (Starting & Normal)

01/23/2014 1:52 AM

The formulas shown in Nema ICS-14 ch. 2.3 TRANSFORMER SIZING are connected to the example presented further[ 2.3.3] This is a transformer dedicated for a pump and does not take into consideration the other load on this transformer. The rated current:

I=MFLA*1.25 as per NEC art. 695.5(A)

The general formula is S [apparent power] =sqrt(3)*VL_L*I[current in A]/1000 [kVA] by definition.

Accurate formula for voltage drop one can see in IEEE-141[Redbook]:

3.11 Calculation of voltage drops

3.11.1 General mathematical formulas

The arithmetic voltage drop V, as defined, is usually considerably less than the absolute value |I*ZT| of the vectorial voltage drop I*ZT.[For three phases system you have to multiply by sqrt(3).]

ZT=ZT%/100*VL_L^2/Srated [ohm] by definition.

Voltage drop[p.u.]=sqrt(3)*ZT*MFLA*k/VL_L= sqrt(3)*ZT%/100*VL_L^2/Srated*MFLA*k/VL_L

Voltage drop[p.u.]= sqrt(3)*ZT%/100*VL_L*MFLA*k /(Srated*1000) [1000*Srated [kVA]=Srated[VA].

During motor running k=1.15 according to NEMA MG-1 ch.12.51 SERVICE FACTOR OF ALTERNATING-CURRENT MOTORS Table 12.4:

For medium motors [ from 1.5 hp up to 500 hp] the service factor is 1.15.

During the start I=6*MFLA [k=6].

__________________
Julius
Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2014
Posts: 8
#5
In reply to #4

Re: Formulas for Voltage Drop of Motors (Starting & Normal)

01/23/2014 8:32 AM

Thanks for your reply, however please advise on the below:

*Definition of MFLA , and its code source

* I didnt get your reply concerning the connection of IEEE-141 to the formulas in my query item (about voltage drops during normal and starting of motor); so please clarify (not in P.U system)

* I didnt find the reference for the factor 6 (K=6)

Thanks

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6

Re: Formulas for Voltage Drop of Motors (Starting & Normal)

01/23/2014 10:26 AM

1)Since the motor ratings are 300 Hp, 460 Volt, 60 hertz and the current mentioned is 361 A this matches the NEC Table 430.250" Full-Load Current, Three-Phase Alternating-Current Motors". NEC defines this current as "Full Load Current -FLC or Motor Full-Load Current [MFLC].

Usually FLA [MFLA] is referring to motor nameplate current.

The actual motor description is in ICS-14 ch.2.1.1 "Example" and in pos.a) the current is named "motor full-load current" but in pos.c) "motor full-load amperes" [it is the same 361 A].

2) In IEEE-141/1993 ch.3.11.1 General mathematical formulas:

"For exact calculations, the following formula may be used:

actual voltage drop= es+IRcosφ+IRsinφ-sqrt(es^2-(IXcosφ-IRsinφ)^2)

where the symbols correspond to those in figure 3-11."

3) In the same above pos. c) it is noted:

"Multiply motor full-load amperes 361 by 6, which equals 2,166 amperes (the locked rotor current of a NEMA Design B 3-phase squirrel cage induction motor is approximately six times the full load current of that motor, and this approximation is used throughout similar examples in this Guide."

__________________
Julius
Register to Reply
Register to Reply 6 comments