Hi all,
I need some help urgently...lol :)
We recently bought a heater (industrial heater ) 230KW 400 Vac 3 Phase .. thyristor controlled ( 2 phases).
The heater consists of 4 groups of heating elements arranged in Delta.
Heating nitrogen with 0,2 ppms of humidity.
Our 400 amp CB tripped on earth fault (set at 300mA).
I measured the insulation resistance @ 500v and got :-
Group 1 = 0.6 M ohms
Group 2 = 0.2 M ohms
Group 3 = 0.1 M ohms
Group 4 = 0.1 M Ohms
I contacted the mantufacture who told me that I had humidity in the elements.. I found this strange if not impossible, (bearing in mind that the heater operated 21 times at 280ºC for a duration of 110 minutes...
they advised me to operate the heater at 15 % load for 24 hrs ... and to measure at ambiente temperature. which I did and got 3,4 M ohms, 1,4 M ohms, 0,4 M ohms and 0,4 M Ohms respectively..
I then measured the same groups at 180ºC and got 0,4 M Ohms, 0.06 M ohms, 0,04 M ohms and 0,03 M ohms
and that is where I get confused.. I think that whether hot or cold the insulation resistance to GND (Earth) has to withstand the applied voltage.. so why I ask is there a difference if I measure when hot or cold ??? I would expect to get a difference in restistor valves between phases but not to eatrh...
Plzzzzzz enlighten me ??