VFD False Shutdowns

03/07/2014 9:48 AM

Hi,

Just a quick brain teaser..

Why would a 45Kw VFD shutdown showing a motor short circuit fault when infact there is none. I reset and the drive may operate 1 day or 2 weeks without shuting down on the same fault.

Today shuting down a plant consisting of two 2500kw 6 kv motors, we had two drives on a seperate area shutdown with the above indicated fault...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#1

Re: VFD false shutdowns

03/07/2014 10:29 AM

Perhaps a mechanical tremor loosens some conductive dust across the mains, enough to trigger a fault ?

Perhaps aging equipment is no longer able to sense proper leakages ?

Perhaps intermittent arcs are being induced by voltage spikes in insulation of old cables ?

For starters, you must assume there is a fault, and search for the most likely cause.

Intermittents are very hard to diagnose, you must consider the environment as well as the age of components and stresses at fault times. Are the motors being started one at a time or is the sequence random, are motors being switched on and off when fault is triggered ?

Careful observation of the environment and operating conditions are sometimes the only way to find such problems. Do you have access to monitoring equipment which can verify the fault ?

Perhaps the only way to find such an intermittent is to take an educated guess and replace a component, and if the intermittent stops then you call it a solve.

Good Luck

L- I -T.

__________________
Smart as a post and twice as fast.
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#2

Re: VFD false shutdowns

03/07/2014 11:50 AM

If push comes to shove, you might try installing an appropriately sized line reactor. Or you could just wait until the short becomes permanate and then you will know that the VFD was trying to help you.

Reminds me of the old story, "Can you spell the VAN in vanilla?"

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: VFD false shutdowns

03/07/2014 12:40 PM

The topology of a 45kW low voltage VSI drive and whatever type of 6kV drives you have can be so vastly different that making a cursory assumption of any kind of common causality is almost ludicrous. But if I had to pick anything that MIGHT be a connecting link, it would be grounding (earthing) practices. If this happens often, I would take a look at how you are running and shielding your output conductors. One misstep and you can create capable cacitance issues that will not show up in common cable installation testing, but can be interpreted by the drive as a Short Circuit, which is typically defined as too rapid of a rise in current over time. If the cables are allowed to store too much energy as a quasi capacitor, the capacitor charging current can look like a short circuit to the VFD protection algorithms.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4

Re: VFD false shutdowns

03/08/2014 12:50 AM

Have you checked the motor bearings and the bearings of whatever that motor is trying to spin yet?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Sep 2009
Posts: 72
#5

Re: VFD false shutdowns

03/08/2014 2:46 AM

Hi,hi, this problem has been happening for quite some time now, we have replaced the motors, adjusted the switching frequency of the drive..

The 6 KV motors are switched on directly.. DOL... but the problem occurs when I shutdown these motors and not when starting..

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#6
In reply to #5

Re: VFD false shutdowns

03/08/2014 3:36 AM

On shutdown......that makes a big difference to your query sport!

That there then would/might be a back EMF problem.

If there's a VFD in there then it's not DOL start then is it?

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2009
Posts: 72
#7
In reply to #6

Re: VFD false shutdowns

03/08/2014 6:51 AM

Read C a r e f u l l y sweetheart !!.... the 6kv 2500 volt motos are DOL, the 45 kW are fed from the drive ...

Register to Reply Score 1 for Off Topic
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#8
In reply to #7

Re: VFD false shutdowns

03/08/2014 10:19 AM

Only if you explain clearly darling.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply Off Topic (Score 4)
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10
In reply to #7

Re: VFD false shutdowns

03/08/2014 7:38 PM

I read it carefully, I think your description was a tad lacking. Remember, you KNOW what you meant, we did not, we can only go by what is entered.

But let's move on. Most likely when your contractor opens on the 6kV DOL starter, it is creating a big spike. If you have capacitors on line with those motors, and the caps are AHEAD of the starter, that spike can be massive. A high energy spike can be interpreted by the smaller VFD protection circuit as a short circuit. For most LV VFDs, short circuit is simply defined as a high dI/dt, meaning delta (change) in current over a delta in time. Basically the current changed too rapidly because of the spike, so the drive assumes the worst and shuts down.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#9

Re: VFD false shutdowns

03/08/2014 10:57 AM

Probably you have long cable between VFD and motor.

And if there are harmonics produced in VFD - at higher harmonics, Xc is very low (1/2 pi * f *C) - resulting in increased leakage and tripping of relay.

you can locate temporarily VFD close to motor,thus shortening length of cable and see if it does not trip. May solve your problem.

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#11

Re: VFD False Shutdowns

03/13/2014 11:50 AM

Please explain what you mean by "shutting down" the motor. Specifically, are you decelerating using a controlled method or are you simply opening the circuit?

There is a world of difference between the two.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (2); LongintheTooth (1); NotUrOrdinaryJoe (2); porky2009 (2); powersolutionsFBD (1); Wal (3)

Previous in Forum: Three Winding Transformer   Next in Forum: How Many of You Have Had Stupid Bosses?

Advertisement