Heat Exchanger Design

06/12/2007 1:55 PM

product entering the tube side of a shell and tube heat exchanger at 40 degrees. it is desired to cool this product to 20 degrees using chilled water at 5 degrees.

how do i calculate the outlet chilled water temperature. i am given the specific heat capacities and mass flow rate. i want to design this shell and tube heat exchanger.

thanx

sarika

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Heat Exchanger Design

06/12/2007 2:40 PM

I would suggest applying the 1st law of Thermo for a control volume.

[ h + 1/2v +gh ]inlet (for each fluid) + Heat(Q) = [ h + 1/2v + gh ]exit (for each fluid) + Work

Also, you must make a few assumptions: - No work(incompressible liquid), No change in velocity, no change in potential. Also if you take your system to be around both pipes and assume no heatloss then Q=0. Therefore you are left with,

m1*[h1]i + m2*[h2]i = m1*[h1]e + m2*[h2]e; now if you have some sort of table, then use that. If not, /\ (change) h = m*cp/\(Temp):

Solve for T2 of water.

Register to Reply
Anonymous Poster
#2

Re: Heat Exchanger Design

06/13/2007 7:55 AM

Use the following formula to calculate the chilled water outlet temperature Toutlet in degree Celcius:

M1 x Cp1 x ((273 + 40) - (273 + 20)) = M2 x Cp2 x ((273 + Toutlet) - (273 + 5))

M1 = Product mass flow rate in kg/hr

Cp1 = Product Heat Capacity, Kcal/kg.degree Kelvin

Make sure that you have the correct units.

Register to Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#3
In reply to #2

Re: Heat Exchanger Design

06/13/2007 12:32 PM

Since the K°=°C it is not necessary to refer to the absolute zero. The equation can be solved in °C only

Register to Reply
Participant

Join Date: Jun 2007
Posts: 3
#4

Re: Heat Exchanger Design

06/13/2007 2:53 PM

if both of the flow rate were known the answer is straight forward by using equation:

Energy balance: Q=mhCph(Thin-Thout)=mcCpc(Tcout-Tcin)

But for this type of problem, usually only one of the flow rates is known. Therefore iteration is required.

Calculation requires tables and charts, but basically there are 2 equations that u should use:

Q=mhCph(Thin-Thout)=mcCpc(Tcout-Tcin) and Q=UA F(LMTD);

F is the thermal correction factor and LMTD is the log mean temperature difference.

correction factor F will determine the type of S&T HE to be used (i.e single pass or multiple pass).

first u should determine/assume the unknown flow rate. Using the 1st equation u will obtain Temp. outlet of the product.

Temp outlet from the first equation is used to obtain Q from the 2nd equation This is where the table and charts come into play, which is to determine U,A and F.

From this point on u should iterate until the Q from the 1st equation is approximately equal to the Q from the 2nd equation. Tout questioned is the Tout that makes this condition possible.

good luck.