Load Calculations

04/10/2014 3:04 AM

Dear All,

I have 3 load (AC) each of 4KW. Supply is 220 V, 50 Hz. Now how do I calculate the amperes. I mean if I consider them as 3 single phase load, the amperes/load are:

4000/220=18.18 amps (neglecting Power factor).

So total amps turn to be 18 x 3 = 54 amps

But if I calculate them as 3 phase, the load is 4KWx3=12KW

so I=12000/(Sqrt(3)*380)=18.23 amps

So why is the difference? Which formula should I consider? Also for Panel Board Selection, I added all the loads, so which formula should be used for the panel board amps?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#1

Re: Load Calculations

04/10/2014 6:26 AM

Both formulas are correct. If you have single phase motors (with single phase supply, obviously) the total supply current is 54 amp as you say.

If they're 3 phase and supplied at 220*√3 = 380 volt, that reduces the amps by √3. But you now have 3 supply lines, which gives another √3 factor, so amps in each line is down by 3.

If the motors are 3 phase and wired for 380 volt star/220 volt delta, (and you have all 6 terminals) you could connect in delta at 220 volt, and line current is then 54/√3 = 31 amp.

You also need to allow for efficiency as well as power factor to calculate current.

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Associate

Join Date: Apr 2014
Posts: 27
#2
In reply to #1

Re: Load Calculations

04/10/2014 6:36 AM

Thanks!

One more doubt, isn't balanced 3 phase load(I mean 3 single phase loads) same as 3 phase load(single unit)?

Also how should I calculate the current of my Panel Board? The total load is 56 KVA. So should I use single or 3 phase formula?

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#3
In reply to #2

Re: Load Calculations

04/10/2014 3:08 PM

One more doubt, isn't balanced 3 phase load (I mean 3 single phase loads) same as 3 phase load(single unit)? If you have 3 motors 4kW each supplied at 220 volt, current to each (ignoring PF and eff) is 18 amp as in your original post. So total current = 54 amp. (Same as for one 12 kW motor). 220volt*3*18amp/1000 = 12 kW.

If the motors are supplied one from each phase of a 3-phase supply, 380 volt to give same 220 volt phase-neutral to the motors, amps to each is still 18. Total power is still 12 kW, as 380*√3*18/1000 = 380/√3*3*18/1000 = 220*3*18/1000 = 12 kW. Same as for one 12 kW 3-phase motor, 18 amp in each line.

Also how should I calculate the current of my Panel Board? The total load is 56 KVA. So should I use single or 3 phase formula? It depends on whether the motors are single or 3-phase (assuming you have a 3-phase supply) and the voltage (see #1). But the total KVA of the 3 motors is still 12kW/PF/efficiency.

__________________
Give masochists a fair crack of the whip
Register to Reply
Associate

Join Date: Apr 2014
Posts: 27
#4
In reply to #3

Re: Load Calculations

04/11/2014 6:46 AM

Thanks bro, really appreciate that!

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #4

Re: Load Calculations

04/11/2014 8:23 AM

No problem, I had to think about it a bit, which was good.

__________________
Give masochists a fair crack of the whip
Register to Reply
Associate

Join Date: Apr 2014
Posts: 27
#6
In reply to #5

Re: Load Calculations

04/15/2014 3:41 AM

Bro, need your help again!

I have a lighting panel board. Obviously all loads are single phase (230 V P-N). Load on phase A is 5 KVA, on B is 4 KVA and on C is 4 KVA.

Total KVA is 13 KVA.Supply volgate is 230/400 V, 60 Hz.

Now, for Cable selection and Protective device for the above panel, I do the calculations as below.

13000/230/0.95=59.5 A

So I would select cable and Protective device keeping in view the above continuous current(i.e. 60 A)

But what I got from the consultant is different. He calculated the current to be:

13000/380/1.732/.96=19.75 A

He also chose the 3 phase cable and protective device accordingly(i.e. for 20 amps).

Why did he use 3 phase formula for single phase loads? What formula should be used in this case both for the cable and protective device??

Thanks

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #6

Re: Load Calculations

04/15/2014 7:38 AM

This is already covered in earlier posts, (with lights in place of 1-phase motors). If all the lights are fed from one single-phase 220V supply, current in each bank is ~ 20A, total ~ 60 A as you say. But if each bank is fed between one phase of a 380V 3-phase supply and neutral, the current to each bank is still ~ 20 A and this is the current in each phase. So the consultant is right.

It might be worth considering the situation when 1 bank is switched off, maybe current in the common neutral is > 20A. I'll try to work it out when I have a minute, but perhaps the consultant knows the answer!

__________________
Give masochists a fair crack of the whip
Register to Reply
Associate

Join Date: Apr 2014
Posts: 27
#8
In reply to #7

Re: Load Calculations

04/15/2014 9:54 AM

This is what confusing me. All lights are single phase and are fed between phase and a neutral(230 V). Total amps are 60. Then how on earch is he selecting MCCB(3phase) with 30 AT/100AF rating. Does 30 AT mean it will trip if current in any phase exceeds 30A or it means that it will trip when total current exceeds 30 Amps?? Also same for the cable.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#9
In reply to #8

Re: Load Calculations

04/15/2014 12:32 PM

As I said in #1, if you had just 1 phase, 220 V, and all loads fed from that, total current is 60 A. But 3-phase 380 V is different, the higher voltage means lower amps (by a factor of 3) and because the currents are out of phase there's another 3, so current is back to 20 A. This is current in each phase of the 3-phase system.

I assume 30 AT/100AF means it is rated for 30 A. I don't know what the 100AF means (I'm not a full-blown electrical engineer!) but it's probably to do with the current needed to trip in a specified time, maybe 0.1 sec. 30 A rating does not mean it will trip at anything over 30 A - see attached link. 30 A is its normal operating current. For fuse protection the link says if the fuse is marked '30 amps', it will actually stand 40 amps for over an hour. That sounds low to me, I always thought fuses blew at ~ 100% overload i.e. 2 x rating, but the principle is the same - the fuse rating is the operating figure, not the rupture current.

http://electrical-engineering-portal.com/what-is-the-difference-between-mcb-mccb-elcb-and-rccb

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#10
In reply to #9

Re: Load Calculations

04/15/2014 3:47 PM

Mistake!

In 1st para I missed out √ in a couple of places. I drafted it in Word as it's been known to get lost from CR4 (probably my fault but still irritating if any length) and forgot to edit after copying in. Corrected below.

As I said in #1, if you had just 1 phase, 220 V, and all loads fed from that, total current is 60 A. But 3-phase 380 V is different, the higher voltage means lower amps (by a factor of √3) and because the currents are out of phase there's another √3, so current is back to 20 A. This is current in each phase of the 3-phase system.

I assume 30 AT/100AF means it is rated for 30 A. I don't know what the 100AF means (I'm not a full-blown electrical engineer!) but it's probably to do with the current needed to trip in a specified time, maybe 0.1 sec. 30 A rating does not mean it will trip at anything over 30 A - see attached link. 30 A is its normal operating current. For fuse protection the link says if the fuse is marked '30 amps', it will actually stand 40 amps for over an hour. That sounds low to me, I always thought fuses blew at ~ 100% overload i.e. 2 x rating, but the principle is the same - the fuse rating is the operating figure, not the rupture current.

__________________
Give masochists a fair crack of the whip
Register to Reply Score 1 for Good Answer
Active Contributor
India - Member - New Member

Join Date: Jun 2014
Location: Chennai, India
Posts: 19
#11

Re: Load Calculations

06/17/2014 8:31 AM

How the hell is 3 single phase the same as a 3 phase?

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#12
In reply to #11

Re: Load Calculations

06/27/2014 9:09 AM

Eh?

__________________
Good moaning!
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Codemaster (6); Crabtree (1); smi_1989 (4); tasneemahmd (1)