Busbar Capacitance Calculation Help and is Transposition Worth It?

04/10/2014 11:51 AM

Hey,

Im looking into a busbar system for a light jet. 28A 115v 400Hz, 1.59mm x 12.7mm three phase copper busbar roughly 9m long with 7.2mm spaces between each bar. However i am unsure on how to calculate the capacitance between these three bars if anyone could send me a link or a forumula to calulate this it would be a big help.

I was also planing to use transposition however without being able to calculate the capacitance Im unsure if it is required. (I also do not know how to work out the capacitance between bars in this formation)

Register to Reply
Pathfinder Tags: Busbar Transposition
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2013
Location: Central Canada
Posts: 677
Good Answers: 28
#1

Re: Busbar Capacitance Calculation Help and is Transposition Worth It?

04/10/2014 3:44 PM

What stops you from building it and measuring it ??

__________________
Smart as a post and twice as fast.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Busbar Capacitance Calculation Help and is Transposition Worth It?

04/10/2014 5:32 PM

The capacitance will be tiny due to the air being the dielectric. HyperPhysics shows the simple math for calculating parallel plates capacitance. I like much better the diagrams from MIT but as you should expect, the math is not as simple.

I almost forgot, if stray capacitance is a problem in your circuit then you do not want air as a dielectric because the humidity and dust levels will change the dielectric constant considerably.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#3

Re: Busbar Capacitance Calculation Help and is Transposition Worth It?

04/11/2014 7:11 AM

Why would you use a busbar system for this application? Clipped direct to the airframe a 3 core 4.0mm² cable will carry 36 amps, and is fully insulated. The additional weight of the insulation will be more than offset by simplification of the mounting brackets, and the flexibility of a cable must help with installation. The cores of a cable spiral around each other so capacitance is not an issue. I would also be concerned about the effect of vibration on rigid busbar connections. A 56 x 0.3mm² multi-stranded core with crimped connections would be far better for this duty.

Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#4
In reply to #3

Re: Busbar Capacitance Calculation Help and is Transposition Worth It?

04/11/2014 7:46 AM

Maybe.

This is an aircraft and the bussing system may be type approved and permit type approved tapping along route.

If it is a type approved bussing system then the capacitance data should be in its specs too.

If it's a replica or prototype then it's back to LCR first principals.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply