Floating Neutral

04/20/2014 6:47 AM

I am at a new project site and I am getting 150 Volts between neutral and earth from the power source. No load is connected yet. And when I connect earth to neutral at the Distribution board this 150 V reduces by 40 - 45 V but doesn't drain off fully. Please suggest some actions by which I get rid of this voltage.

Gowin Pande

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#1

Re: Floating Neutral

04/20/2014 9:19 AM

With the only load on the line being a high input impedance voltmeter you can get all sorts of unusual voltage readings. Then again you might have a more serious problem like excessive leakage paths from a shoddy installation (dirt, broken insulation, salt or other electrolyte water, etc.) or even faulty equipment. Identify your neutral grounding standard for your location. You should also realize that you always do have a neutral grounding resistance, regardless of somebody designing one in. If no resistor or cable has been connected between Earth and neutral then the cabling insulation resistance between Earth and ground will also exist between your hot wires and ground.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Floating Neutral

04/20/2014 9:35 AM

Disconnect all the wires, then check again when the wires are empty.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3

Re: Floating Neutral

04/20/2014 12:36 PM

Isolate the supply and have the installation inspected for safety by a qualified Electrician before re-energising, Agnes. You know it makes sense.

__________________
Good moaning!
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jan 2011
Location: Jakarta
Posts: 162
#4

Re: Floating Neutral

04/20/2014 10:18 PM

if you have 3phase lv system, do check L-N and L-ground. Do not short to ground if you have leakage voltage like this, it dangerous. Some earth point may be connected on body of device. Make sure everything safety

__________________
One system
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: Floating Neutral

04/20/2014 11:15 PM

Friend,

If you have a 120-volt (or similar) incandescent light bulb in a socket with leads, you can connect it between the neutral and ground. It will provide a fairly low resistance path between the two. If you have a truly faulty system, this bulb will light; but if you just have a lot of impedance or capacitive coupling then the bulb will stay dark and the voltage you measure will be much lower.

My opinion is that this new system does not have a properly grounded transformer at the source (neutral tied to the transformer frame and both bonded to a good ground (rod, buried structural steel, or similar).

--JMM

Register to Reply
Member

Join Date: May 2013
Posts: 5
#7
In reply to #5

Re: Floating Neutral

04/21/2014 2:13 AM

Thank you very much. today I have called the Electricity Board persons to check their neutral and whether it is grounded properly or not.

Regards,

Gowin Pande

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #7

Re: Floating Neutral

04/21/2014 3:17 PM

If you're calling the electricity board to check the transformer why are you suggesting in a later post #8 you are planning to ground the neutral.

If the transformer belongs to the EB it is not your responsibility. Don't interfere with it.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: May 2013
Posts: 5
#11
In reply to #10

Re: Floating Neutral

04/22/2014 2:54 AM

You are right. But, EB person has also suggested the customer to earth the neutral.

Thanks & regards,

Govind Pande

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12
In reply to #11

Re: Floating Neutral

04/22/2014 6:47 AM

Sorry, but it is the electricity boards responsibility to maintain an effectively earthed (grounded) neutral. Stand your ground on this (OK a bad choice of words).

You start taking responsibility and any later problems, accidents or what ever, become your problem. A problem that could land you in a court of law.

Do you have this request to provide the neutral point earthing from the electricity board in writing? I very much doubt it, they aren't that stupid.

Drop the whole idea.

Put the ball back in the electricity board's court.

I'm not criticising you, I'm trying to keep you out of a whole heap of trouble and litigation.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2006
Location: Australia
Posts: 269
Good Answers: 1
#13
In reply to #12

Re: Floating Neutral

04/22/2014 7:30 PM

I think it might depend on where you are located. In Australia, every consumer has a MEN (Main Earth Neutral) link, connecting the neutral to the earth at the switchboard. From what you are saying, it's obviously different in different countries.

__________________
An engineer is a man who can do for five bob what any bloody fool can do for a quid (Neville Shute)
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#14
In reply to #13

Re: Floating Neutral

04/22/2014 11:58 PM

It would help if we knew the location of the OP. And that's up to the OP to let us in on the secret.

That said, from the figures given the electricity companies earthing arrangements aren't really up to the standards one you would expect for a new project.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Apr 2014
Posts: 51
#6

Re: Floating Neutral

04/20/2014 11:43 PM

I personally faced such problem then i used a separate earth pit for the grounding the neutral and problem get sortout

Register to Reply
Member

Join Date: May 2013
Posts: 5
#8
In reply to #6

Re: Floating Neutral

04/21/2014 2:17 AM

thanks. I have also got the similar plans to ground neutral to a seperate earth at the source.

Regards,

Gowin Pande

Register to Reply
Associate

Join Date: Aug 2013
Posts: 31
Good Answers: 3
#9

Re: Floating Neutral

04/21/2014 7:59 AM

I have experienced this a few times in my life. It is my opinion that you have an open short in one of your primary lines. Each time I saw this it was the insulation on the wire was damage where it passes through the panel to the meter base. Since the primary is fused behind the panel by the power company, you are not creating large enough short to cause any concerns for them. You have proven this by your statement that "no load is connected yet" . I am assuming you have the main disconnected. If true, your meter should be turning, indicating you are using power. If it is, you have a shorted primary. In addition the panel is most likely warm to touch!

Best Luck!

Register to Reply
Anonymous Poster #1
#15

Re: Floating Neutral

04/26/2014 3:18 AM

during project We have same problem in output of our UPS which neutral is floating and we decided to use isolation transformer and grounded the neutral on secondary side .

Register to Reply
Register to Reply 15 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); catman58 (1); Crabtree (1); Gowin Pande (3); jmueller (1); loadshare (1); lyn (1); navdeep_goyal (1); nutwood (1); redfred (1); TonyS (3)

Previous in Forum: How to Calculate Cable Size   Next in Forum: Duty Type of Universal Motor

Advertisement