Previous in Forum: LEROY SOMER 11 KV ALTERNATOR LS54A   Next in Forum: explosion proof inverter!
Phasor sum
06/23/2007 1:36 PM
Hi
I want to use a PLC to detect a phase shift between two vectors.
I want to find a vector sum of two values.
Pls who can help how to detect the phase shift ?
Pathfinder Tags: phasor sum. electrical PLC
Re: Phasor sum
06/24/2007 3:57 AM
Hello,
I think you should give some more info to get an answer you can use.
What kind of vectors?
Do you have two pairs of complex numbers or two analog voltages ??
Regards Uwe
The sum of intelligence on earth is a constant. And the population grows and grows and .....
Re: Phasor sum
06/24/2007 4:54 AM
Hellow uweka
Thank you for your comment.
I want to measure two analog voltage values.
thanks
Re: Phasor sum
06/24/2007 7:34 AM
Hi,
mathematically you have
u1=U1p*cosωt
u2=U2p*cos(ωt+φ2) with
Up=√(U1p²+U2p²+2*U1p*U2p*cosφ2 and
φ=arctan((U2p*sinφ2)/(U1p + U2p*cosφ2)).
For Up: I would get the peak values with an ADC.
For φ: I would use a zero crossing comparator to get the phase signals of U1 and U2 and then make a time measurement of a) the signal period and b) the delay U1 to U2.
Regards Uwe
Re: Phasor sum
06/25/2007 12:28 PM
To get peak value of your measured voltage
Time's (*) RMS value by 1.414
________________________
Thank you and good night
Register to Reply 4 comments