Underground Cable

05/29/2014 1:26 AM

Is there any difference of insulation level for 3 core & single core u/G cable e.g. Thickness of XLPE, semiconducting layer etc for same cross section area of conductor.

Register to Reply
Pathfinder Tags: underground cable
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Underground cable

05/29/2014 2:25 AM

Come on, Mildred. Make a phone call or two to a couple of cable suppliers!

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Apr 2011
Location: KCM, chingola; copperbelt; zambia; southern africa.
Posts: 75
#2

Re: Underground cable

05/29/2014 8:35 AM

you need to go underground see the environment, the see how foolish it will feel to ask such a question. temps are high and its wet.

__________________
an error does'nt become a mistake if corrected!
Register to Reply Off Topic (Score 3)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Underground Cable

05/29/2014 12:46 PM

In my opinion the insulation thickness , conductor shield and insulation screen -and all other parts -except armour and serving - are the same for the same rated voltage.

In USA U.L. standards state the cable building rules .See:

UL Standard 1072 Standard for Medium-Voltage Power Cables

For IEC world see: IEC 60502-2 Cables for rated voltage from 6 kV up to 30 kV.

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Underground Cable

05/29/2014 3:41 PM

Yes and no depending on the application.

Try looking at cable manufacturer's websites for more details.

__________________
jack of all trades
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#5

Re: Underground Cable

05/30/2014 12:16 AM

In India it is NO . Special considerations can be paid by the owner if one needs to. But yes, As all around the world the cable capacity gets de-rated.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 79
#6

Re: Underground Cable

05/31/2014 1:12 PM

Insulation thickness of ue rated cables higher than earthed system cables due to sqrt^3 times higher voltage between phases during earth fault in unearthed system

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7
In reply to #6

Re: Underground Cable

06/22/2014 2:45 AM

You are right, tigerdon. The grounding fault duration state the insulation thickness.

From IEC 60502-2 ch. 4.1 Rated voltages:

"The rated voltage of the cable for a given application shall be suitable for the operating conditions in the system in which the cable is used. To facilitate the selection of the cable, systems are divided into three categories:"

Category A: ground fault is disconnected from the system within 1 min.

Category B: ground fault is disconnected from the system within 1 h. [up 8 hours could be tolerated if the total duration in one year should not exceed 125 hours.]

Category C: [more than category A or B].

Table 1 presents the recommended rated voltage-to-ground [or neutral] Uo. For category A and B it will be a half of maximum permitted phase-to-phase. For C category more is required.

Category A corresponds to 100% and Category B to 133% insulation level according to UL 1072.

__________________
Julius
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (2); Crabtree (1); DmanEng (1); jack of all trades (1); M.R.Iyengar (1); tigerdon (1)

Previous in Forum: Transformer- Find Location of Partial Discharge   Next in Forum: New Battery for Laptop, Commissioning

Advertisement