06/14/2014 2:25 AM
Hi Guys,
Why do the electrical earthing system need to have at least 2 earth chamber with earth rod and in ring formation before connecting to the main earth terminal?
To reduce the overall resistance?
Sorry not a electrical guy.
Re: Electrical TNS Earthing system
06/14/2014 5:13 AM
Need?
Good moaning!
Good Answers: 181
Re: Electrical TNS Earthing System
06/14/2014 4:16 PM
Sorry not a electrical guy?
TNS = Terra Neutral Separate
Not many non electrical people would know that little gem. Methinks you know the answer Mr. Anonymous.
06/16/2014 8:49 AM
Staying Anonymous doesn't mean I know the answer, replying doesn't mean you know the answer.
Thank you for your time.
Good Answers: 445
06/14/2014 10:09 PM
Can you spell "redundancy"?
06/16/2014 8:51 AM
Thank you.
06/15/2014 12:46 AM
Ring circuit(earth or sockets)ensures reliablity even if one of the two wires on the ring breaks.
pnaban
06/16/2014 8:51 AM
Thank you
Good Answers: 117
06/15/2014 6:11 AM
Good question. Please sign up to the forum, and you will likely get a good answer.
(we need more people like you who are honest about what they don't know, and are willing to meet us half way.)
And no, in answer, I have no freakin' idea why the ring...grin!
06/16/2014 8:52 AM
Thank you
Belgium - Member - New Member
Good Answers: 21
06/17/2014 4:37 AM
IEC 60364 distinguishes three families of earthing arrangements, using the two-letter codes TN, TT, and IT.
The first letter indicates the connection between the power-supply equipment (generator or transformer) and the earth.
  • "T" - Direct connection of a point (wye point) with earth (Latin: terra)
  • "I" - No point is connected with earth (isolation), except perhaps via a high impedance.
The second letter indicates the connection between casing / housing / the earth point of the electrical device being supplied and the earth.
  • "T" - Direct connection of a point with earth
  • "N" - Direct connection to neutral at the origin of installation, which is connected to the earth
  • "U" - Metallic casing are connected with each other, but not intentionally with the earth.
  • "M" - Metallic casing are connected with each other and connected with the supply wye point, but not intentionally with the earth.
In case of a third or a fourth letter; this indicates the design of the neutral line and/or the protection line (earth connection line)
  • "S" - the neutral and the earth connection line are separated wires (S = separation)
  • "C" - the same wire is used for neutral and earth connection line (C = combined)
Good Answers: 42
07/16/2014 1:11 AM
I agree with you, rudy.leurs: IEC 60364-1 is referring to TNS as one earthing type system- with a separated PE grounding conductor. But, it seems to me, the OP was referred to "earth chamber". Maybe one of these:
An "earth chamber" is employed to connect a grounding-vertical-rod with a horizontal grounding cable and for testing the grounding rod. Why we need 2 of these? In a substation or in a power station could be a hundred, depends of how many grounding rods one needs. The modern grounding system is using cadweld-or other welding technology-and it doesn't need "earth chambers".
The foundation grounding- and earth ring-see:
http://en.wikipedia.org/wiki/Ring_ground
Julius
Good Answers: 42
07/16/2014 1:20 AM
The "earth chamber" image did not appear. I'll try one more time.
Julius
07/20/2014 1:21 AM
I guess you are in the U.K. We don't use a ring system in OZ, so I am saying you don't NEED a ring system unless it is mandated by legislation.
Jim