Dear All,
I needed a clarification on a 300kVA ZigZag Transformer used in the following scenario...
We have a 11kV Switchboard feeding a 11/132 kV 35MVA transformer. This 11kV switchboard is fed by 7 No.s of 0.66/11kV 4.5 MVA (YNd11) Transformers as incomers to Switchgear through VCB's. Inturn the 4.5 MVA transformers are fed by 0.66 kV, 1MW alternators .ie we are stepping up a Generation voltage of 0.66 kV to 11kV by 4.5 MVA trf and feeding to 35 MVA trafo through switchgear. We also have a 300 kVA Zigzag Trafo connected to the 11kV Switchgear and a 11/.415 kV 1.25MVA (Dyn11) service Transformer which feeds the auxiliary loads of the alternators.
Kindly clarify whether the Zigzag Transformer will remain connected to the 11kV Switchgear during the normal operation of the system .i.e when the Incomer VCBs are closed or will be taken out of service or ZIGZAG TRF'S are connected only when it is intended to provide a low resistive path to neutral current for an Earth Fault occuring in the Delta side / ungrounded 3 Ph system i.e when the Incomer VCBs are open and only when the Dyn11 Service Transformer is feeding the auxiliaries. Please clarify.
If it is provided with an intent to provide a low impedance return path for a Ph-Earth Fault or an unbalance occuring in the Delta side or Ungrounded 3Ph system, can't the Dyn11 1.25 MVA Delta- Star Service transformer do that job.
"Almost" Good Answers: