Clarification on Zigzag Transformer

06/25/2014 12:09 PM

Dear All,
I needed a clarification on a 300kVA ZigZag Transformer used in the following scenario...
We have a 11kV Switchboard feeding a 11/132 kV 35MVA transformer. This 11kV switchboard is fed by 7 No.s of 0.66/11kV 4.5 MVA (YNd11) Transformers as incomers to Switchgear through VCB's. Inturn the 4.5 MVA transformers are fed by 0.66 kV, 1MW alternators .ie we are stepping up a Generation voltage of 0.66 kV to 11kV by 4.5 MVA trf and feeding to 35 MVA trafo through switchgear. We also have a 300 kVA Zigzag Trafo connected to the 11kV Switchgear and a 11/.415 kV 1.25MVA (Dyn11) service Transformer which feeds the auxiliary loads of the alternators.
Kindly clarify whether the Zigzag Transformer will remain connected to the 11kV Switchgear during the normal operation of the system .i.e when the Incomer VCBs are closed or will be taken out of service or ZIGZAG TRF'S are connected only when it is intended to provide a low resistive path to neutral current for an Earth Fault occuring in the Delta side / ungrounded 3 Ph system i.e when the Incomer VCBs are open and only when the Dyn11 Service Transformer is feeding the auxiliaries. Please clarify.

If it is provided with an intent to provide a low impedance return path for a Ph-Earth Fault or an unbalance occuring in the Delta side or Ungrounded 3Ph system, can't the Dyn11 1.25 MVA Delta- Star Service transformer do that job.

__________________
"Engineering is Passion"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Clarification on Zigzag Transformer

06/25/2014 10:43 PM

The answer to your question requires knowledge of your protective relaying scheme and the local codes in effect where this will be operated. Asking the question implies you lack both. Hire a competent engineering consultant to guide you.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Clarification on Zigzag Transformer

06/26/2014 2:51 AM

In a previous thread started by our OP he stated he was a junior engineer in a power plant. It would be reasonable to assume there are more senior engineers that should really be giving guidance to a junior.

So why ask a group of random guys?

Am I being cynical?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#3
In reply to #2

Re: Clarification on Zigzag Transformer

06/26/2014 8:28 AM

Dear All,

Than you very much Gentlemen for sparing time to answer my question, though not in a way I expected.

Mr. Tony was right, I was working as a JE in a TPP. But I find myself in an unfortunate position where I cannot seek support of my Seniors for getting my doubts clarified. I have to rely on books/ online support by myself and Technical forums like CR4 and others to get it clarified by Unknown faces and I am happy that in the past many concerned and generous Engineers have helped me. I may not have a strong Design Background as my experience is in site activites and PM, but I do look upon 'EXPERTS' like you guys in the forums to know more. I am not gonna stop posting question I don't know the answer, If you know the answer please help me out, otherwise please dont mock others in public forum. CR4 is not only for experts but also for budding engineers like me I believe...

Thanks once again..

__________________
"Engineering is Passion"
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: Clarification on Zigzag Transformer

06/26/2014 3:56 PM

Your descrioption is a bit run-on, and I can see that English is probably not your native language, but I respect that you have tried to give a detailed description of your system. A single-line diagram with nameplate info on the various pieces of apparatus could help, but based on what you described, I would say the following:

1. If the 11kV portion of the system has ONLY delta windings connected to it, then you need the zigzag transformer to provide a ground source so that ground fault relays can operate. GF relays will not look through a transformer, so a grounded neutral on the other side of the windings (such as the 415V side of the station service transformer) does not give you a ground reference.

2. If there is a Wye winding (having a grounded neutral) on the 11kV bus, then you don't need the zigzag when the wye is connected. If the breaker for the wye winding transformer is open, then the zigzag is needed.

3. You didn't give the winding configuration of the 11/132kV transformer, but I assume it's Delta on the 11kV side and wye on the 132kV. That is the standard approach on a GSU transformer. If the 11kV is wye, then you don't need the zigzag. However, I assume you have the zigzag just because the main transformer is delta-wye.

I hope this helps.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Dec 2010
Location: Chennai
Posts: 40
#5
In reply to #4

Re: Clarification on Zigzag Transformer

06/27/2014 1:59 AM

Dear Sir,

Thank you very much for that update. As correctly stated by you the GSU trf is YNd1 winding trafo.

My sincere thanks to you once again for helping me out.

__________________
"Engineering is Passion"
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PeterT (1); Raghavendran R (2); RAMConsult (1); TonyS (1)

Previous in Forum: Base Value of LA LCM   Next in Forum: Keyence Vision

Advertisement