Neutral Grounding Resistance

06/27/2014 1:50 AM

We have a bank of 11KV 2000KVA DG sets operating in parallel with the grid. The DG set neutrals are grounded through resistance to limit ground fault current to the full load current of the generators, Only one neutral is connected to ground when sets are operating in parallel. The complication comes when the sets are paralleled with grid. The supply company wants their transformer neutrals to be solidly grounded. If we remove the DG neutral from grounding when the DG sets are grid paralleled then we are subjecting the DG alternators to heavy ground fault current in the event of a ground fault. If we remove the transformer neutrals from ground and keep the DG resistance grounding in circuit then it is unacceptable to supply company. Could some one with similar experience illuminate how this situation can be handled?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Neutral Grounding Resistance

06/27/2014 11:43 PM

>Deleted<

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#2

Re: Neutral Grounding Resistance

06/28/2014 12:53 AM

Please provide an annotated sketch of your setup and identify exactly where the ambiguity or contrary/conflicting standard interpretation is.

Too many words to digest Learner!!! A lot of us here are old and what time we have left we like to use efficiently....get to the point young dude.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Commentator

Join Date: Jan 2014
Location: Korba, Chattisgarh, India 495450
Posts: 64
Good Answers: 2
#3

Re: Neutral Grounding Resistance

06/28/2014 2:25 AM

Yes, Apparently there is an issue.

It is true that only one grounding system should be functioning to cater tio entire system but the same is not capable in this case. By grounding differently neutral voltages differences shall lead to circulating currents and heating. there needs to be some investment of some mind-game into it. Could you provide sketch - block dia atleast with parameters. Let us think on it.

__________________
Let us discuss the practical issues not the classroom.
Register to Reply
Guru

Join Date: Apr 2012
Posts: 732
Good Answers: 17
#4

Re: Neutral Grounding Resistance

07/07/2014 1:49 PM

Use the Gennies as separately derived sources

...or...

Change the neutral bonding method on the gennies

__________________
common knowledge...less common than common sense
Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

M.R.Iyengar (1); The.Tinkerer (1); TonyS (1); Wal (1)

Previous in Forum: Lux Level for Outdoor Plant   Next in Forum: 3 Phase Voltage

Advertisement