Frequency Variation in 50 Hz Transformer

06/28/2014 8:04 AM

Hi,

normally, in a single phase transformer, as frequency is increased, iron losses increases as hys loss and eddy loss increases.

But, i see in book - when 25 Hz transformer operates on 60 Hz, iron losses are decreased by 25%. How is this possible?

Regs

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: frequency variation in 50 Hz transformer

06/28/2014 8:49 AM

tasneemahmd

Read further in the book and let us know! Which book is it anyway?

__________________
Common Sense Dictates
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Frequency Variation in 50 Hz Transformer

06/28/2014 12:44 PM

It be magic Jim, plain and simple.....

http://www.edaboard.com/thread261091.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #2

Re: Frequency Variation in 50 Hz Transformer

06/29/2014 10:04 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #5

Re: Frequency Variation in 50 Hz Transformer

06/29/2014 12:05 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#3

Re: Frequency Variation in 50 Hz Transformer

06/29/2014 12:36 AM

Iron losses DECREASE with frequency increase. This is why standby generators on airplanes are 400 HZ to cut down on core weight of the generator. I designed transformer for years and the 50Hz core had to be larger than 60 Hz cores. The book is correct about the 25 Hz.

Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#4

Re: Frequency Variation in 50 Hz Transformer

06/29/2014 8:02 AM

I think the answer is that for a given core size, you can get more power through a transformer at a higher frequency. 400 hertz transformers are smaller for a given power rating, which is why 400 hertz is used in applications such as aircraft where weight is important. Audio transformers are smaller and RF transformers much smaller.

The amount of hysteresis power loss increases with frequency:

Ref: http://en.wikipedia.org/wiki/Transformer#cite_note-Heathcote.2C_pp._41-42-47

"Hysteresis lossesEach time the magnetic field is reversed, a small amount of energy is lost due to hysteresis within the core. According to Steinmetz's formula, the heat energy due to hysteresis is given by, and,hysteresis loss is thus given bywhere, f is the frequency, η is the hysteresis coefficient and βmax is the maximum flux density, the empirical exponent of which varies from about 1.4 to 1 .8 but is often given as 1.6 for iron."

Bottom line: Increase in power loss does not necessarily mean lower efficiency. If the increase in power transferred is even greater, the efficiency can be higher.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Frequency Variation in 50 Hz Transformer

06/30/2014 10:37 AM

According to [for instance]:

NASA TECHNICAL NOTE [NASA TN D-3114]:

HYSTERESIS AND EDDY-CURRENT LOSSES OF A TRANSFORMER LAMINATION VIEWED AS AN APPLICATION OF THE POYNTING THEOREM by John Barranger Lewis Research Center Cleveland, Ohio:

".....according to Maxwell's equations the total loss or core loss is

Pc = Ph+ Pe formula (9) where Ph is the hysteresis loss and Pe is the eddy-current loss."

Ph=kh*Bm^2*f formula (58)

Pe=ke*Bm^2*f^2 formula( 40-42).

If supply voltage remains the same, for the same column cross section area:

B1*f1=B2*f2

PW1 =kh*B1^2*f1+ke*(B1*f1)^2

Pw2=kh*B2^2*f2+ke*(B2*f2)^2 and if we shall use B2=B1*f1/f2 we shall get:

Pw2=kh*(B1^2*f1)*f1/f2+ke(B1*f1)^2

That means eddy current loss remains constant but hysteresis losses decrease by f1/f2.

If f1=25 Hz and f2=60 Hz the hysteresis losses will be 25/60=0.417 [only 41.7%].

__________________
Julius
Reply
Anonymous Poster #1
#9
In reply to #7

Re: Frequency Variation in 50 Hz Transformer

07/15/2014 12:04 AM

1. could not quite get how eddy current remains constant.

Regs,

Reply
Active Contributor
India - Member - New Member

Join Date: Jun 2014
Location: Chennai, India
Posts: 19
#8

Re: Frequency Variation in 50 Hz Transformer

07/11/2014 9:10 AM

Thats what I meant by funny. Broaden your view, will ya?

http://www.carbonlighthouse.com/2011/03/03/three-phase-power/

Btw, I am not the OP for this one.

Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); 7anoter4 (1); Anonymous Poster (1); IdeaSmith (1); Rixter (1); SolarEagle (3); tasneemahmd (1)

Previous in Forum: Using a European Motor Appliance (Vacuum Cleaner) on Two-Phase 240V US Supply   Next in Forum: Electrical Smart Designer Application

Advertisement