Hi guys, I am about to do a job where I have to run 12 x 240mm single core cables to supply 4 motors. Will the trefoil stacking of ; RWB RWB RWB RWB ..... W being on top. be ok? Or do I have to have a different configuration? Any advice appreciated!
Pathfinder Tags: Multiple trefoils
Re: Running cables in trefoil.
07/25/2014 6:10 PM
07/25/2014 9:43 PM
Thanks lyn... Will the the configuration of RWB RWB RWB RWB be ok tho?
07/25/2014 10:04 PM
Does it really matter? See above.
Will the motors rotate in the desired direction?
Good Answers: 181
07/25/2014 10:02 PM
Over long runs you're supposed to alternate the order. Over the years I've used straight and interleaved methods, I can't say I've ever noticed any difference in temperature. It makes the install difficult and looks a mess.
For long runs in trenches I've run singles in hardwood cleats giving equal spacing. It made installation easy and gave good ventilation.
Please don't tell me you're going to use nylon lock straps to secure them.
I will say I've never run singles to a motors only for transformers
Good Answers: 42
07/26/2014 12:51 AM
Since you have 12 single-core cables for 4 motors then you have-for each motor-only one conductor per phase. In this case- actually- it is not important the cable sequence in a bunch of three. The unbalance could occur only between more parallel cables -per phase.
Julius
07/26/2014 1:33 AM
All sorted out. Thanks for your time guys! Much appreciated.