Anonymous Poster #1

Short Piece of Cable Used in Outdoor Substation

08/11/2014 10:57 PM

Good morning to all, I have noticed, in most substation there is short piece of cable used for transformer HT Connection and this cable is rapped At outdoor pole mounted transmission line. My query is why we use this short piece of cable when we can connect transmission conductors directly to transformers. Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Short Piece of Cable Used in Outdoor Substation

08/11/2014 11:19 PM

Because a long one isn't needed.

Do you know why some power is generated at 42 Hz?

Reply
Power-User

Join Date: Jun 2008
Location: Kentucky Lake
Posts: 390
Good Answers: 26
#3
In reply to #1

Re: Short Piece of Cable Used in Outdoor Substation

08/12/2014 1:46 AM

Also, when they used a long piece of cable, people kept tripping on it.

Reply
5
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#2

Re: Short Piece of Cable Used in Outdoor Substation

08/12/2014 1:37 AM

I think from your description that it is necessary to isolate the transformer lugs from the direct tension they would have if they were connected directly to the transmission lines.

Basically, the lines are in tension onto the end insulators. The short piece of wire/cable that you describe connects the line (electrically) to the transformer while the mechanical strength necessary to support the line is carried on the insulator/termination.

This also isolated the transformer from other strain when the HT lines move in the wind, or due to thermal expansion, or due to shock when ice falls off etc.

I truly hope that I've understood your question correctly.

__________________
Just an Engineer from the land down under.
Reply Good Answer (Score 5)
Guru

Join Date: Aug 2009
Location: Glen Mills, PA.
Posts: 2385
Good Answers: 114
#4

Re: Short Piece of Cable Used in Outdoor Substation

08/12/2014 1:36 PM

Just adding to JAE's excellent explanation, the last pole or structure is called a "Dead End" structure, it is strong enough to hold the full tension on one side without a balancing load on the other side; the short piece of cable is referred to as a "Slack Span". The slack span is short so that it does not have to be tight to keep it at sufficient clearance above other equipment and people: because it isn't tight, it doesn't pull the connections off the transformer.

__________________
In a time of universal deceit, telling the truth is a revolutionary act. George Orwell
Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#6
In reply to #4

Re: Short Piece of Cable Used in Outdoor Substation

08/13/2014 7:32 PM

And I might add the slack span line drop into the substation should include a connection to the line end of a station class surge arrester ahead of, and in parallel with, the transformer bushing.

Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#5

Re: Short Piece of Cable Used in Outdoor Substation

08/13/2014 12:49 PM

Transmission lines are never connected directly to equipment due to forces acting on the conductor. The droppers, open ali conductor is terminated on a landing structure and these short ali conductors can be removed to isolate the line from equipment.

Connecting the indoor switchgear to the transformer outside, one cannot use open conductor for obvious reasons, BUT, if the conductor is going inside a building, a rather large wall mounted busing is required, and these are expensive, very large, heavy and a wall needs reinforcing to support it. Inside the building one requires a lot of clearance for the indoor conductor so that makes it expensive to build a huge building to offer clearances to ground. ABB makes these bushing for HVDC converter stations and the bushing that was delivered today on a semi trailer is longer than the trailer itself and approximately 1.4m in diameter at its thickest point.

If it is indeed an insulated cable of 1 or 3 core construction, it does the same thing, offers an point to isolate the equipment in the yard to the indoor equipment and offers a circuit to the indoor equipment. Outdoor equipment is normally connected via a strung ali busbar or an ali tube busbar which runs overhead. I have built subs with busbar going from outdoors to indoors, via an insulated wall section, bushings and onto the indoor busbar system, on to the switchgear. It is costly and cumbersome and easily short circuited by birds, cats, rats, people, vehicles and ladders.

That is the gist of it, costs, maintenance, turn around time for failures, protection of equipment from fault forces and it a line falls down, it does not wreck the equipment by ripping out bushing, The line and droppers snap normally and save the expensive yard equipment, CB's, Tfx, Isolators,surge arrestors etc.

Reply
Reply to Forum Thread 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Barchetta (1); Bluestone (1); IQ (1); Just an Engineer (1); lyn (1); passingtongreen (1)

Previous in Forum: Solar 12V 24V 30 Amp Battery Controller   Next in Forum: Regarding Load List For Any Plant

Advertisement