Subtransient Reactance of Generator

08/15/2014 1:42 AM

Somebody can tell me . If I have generator of 3.2 mva ,voltage rating 415V,and reactance is 12.5% then how i calculate generator subtransient reactace Xd"? Please give me a formula?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: subtransient reactance of generator

08/15/2014 2:52 AM

try to search for:

"subtransient reactaNce"

This will get you further!

__________________
Common Sense Dictates
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#2

Re: subtransient reactance of generator

08/15/2014 8:13 AM

I guess 12.5% you mentioned is the Xd', check the name plate!

__________________
Raghunath
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3
In reply to #2

Re: subtransient reactance of generator

08/15/2014 12:02 PM

X'd is not the same as Xd, this is engineering science, not political science, guessing is inappropriate.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Subtransient Reactance of Generator

08/15/2014 12:12 PM

You can't. This is not an exercise for handbook engineers, nobody can tell you except the manufacturer.You could use guesstimates (see above), but since X"d is a critical parameter in stability and short circuit studies, an error in your "guess" could result in a false sense of stability and/or undersized protective equipment.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: Jul 2013
Location: Faridabad Near New Delhi India
Posts: 240
Good Answers: 34
#5

Re: Subtransient Reactance of Generator

08/15/2014 11:14 PM

A value of 12.5% of transient reactance for rating of alternator seems low, until the alternator was a special ordered oversized alternator for applications such as too much non-linear loads or to cope up with voltage dip while starting a motor.

Otherwise I am not aware of any calculations, Xd" and Xd' are determined by testing during shop tests (sudden short circuit test say at 50% of rated voltage).

In case Xd" is not available a good guess can be 50% of Xd'. My experience with 100s of small 3 phase salient pole synchronous alternators is that Xd" is approximately 50% of Xd'. This shall be a conservative figure for maximum fault or peak fault current calculations, as even IEC permits a Tolerance of +/-20% in these parameters.

Register to Reply
Associate

Join Date: Aug 2014
Posts: 35
#6

Re: Subtransient Reactance of Generator

08/17/2014 6:41 AM

Thank u all for the replies.I understood that subtransient reactance of generator will be mentioned by manufacturer.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Subtransient Reactance of Generator

08/17/2014 12:44 PM

The synchronous generator reactance of 12.5% could be X"d [subtransient reactance] but only if it is a salient poles machine. See ABB Switchgear Manual 11 ed. ch. 3 Calculation of Short-Circuit Currents in Three- Phase Systems. Table 3-6 Reactance of synchronous machines.

__________________
Julius