is there any way or formula to find the active power drawn by the power factor correction capacitor?and also why it should be switched off at no load condition
Good Answers: 137
Re: active power drawn by capacitor
09/04/2014 6:53 AM
Somebody might correct me, but I believe no active power is drawn by a pure capacitance. Not sure about 2nd question, but I suppose when the equipment is switched off or at no load the capacitor would affect the power factor of the complete system, maybe causing a leading PF, which isn't desirable.
Re: Active Power Drawn By Capacitor
09/04/2014 8:13 AM
find the capacitor's specified value for
loss factor = tan delta
and multiply it by the reactive power.
This will give you active power = power loss.
Good Answers: 444
09/04/2014 10:42 AM
I guess you missed the lecture on power measurement. Use a precision wattmeter to measure the loss.
The lecture that you missed on basic AC circuit theory would have taught you that capacitors are used to raise the voltage on loaded lines, and that when the lines are unloaded and the capacitors are still there then you might raise the voltage beyond the equipment ratings.
Good Answers: 128
09/05/2014 12:51 AM
harshipatel,
In addition to the answer by RAMConsult, to raise the voltage on the lines, capacitors are very often used to correct the power factor. Typical industrial loads have a significant inductive component, so the current and voltage are out of phase to each other. (Mathematically, the power factor is the cosine of the phase angle between voltage and current waveforms.) This results in significant inefficiencies in transformers and on the circuits and power lines. Capacitors, as you would learn in basic AC theory classes, have the opposite effect on the current and voltage relations (compared to inductors such as motors). Thus, a properly-sized capacitor bank will correct nearly all of the power factor problems caused by inductive loads.
Now, when the inductive load is turned off, a connected capacitor bank will tip the power factor the other way, which is equally bad (and can raise the circuit voltage). That is the primary reason why they are switched off at no-load conditions.